I have a 2000sq/ft bilevel built in 2001, air filter is new, heat off delay is set 140 sec... it heats the house about +8 degrees per hour...
I run 65 when i'm home (or about 8hrs a day) and 58 the rest of the time, it still consumes 4 ccf's per day! (ambient temps 15-30f), I have 18" of cellulose in the attic, double pane windows no drafts etc
anything to check with the unit itself? I get about 115f out of the registers, blower is set MEDIUM HIGH / ORANGE per the label on the furnace door
ls3c6 is offline   Reply With Quote
Old 12-19-2009, 12:43 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 2,286
Your temp rise sounds okay at 115 (50F) so the unit is producing the right amount of heat. Ever had an energy audit done on the house to check for leaks etc? Some companies use an infrared camera and it is surprising to see the results. Where do you live?
Old 12-19-2009, 01:03 PM   #3
I live in West Michigan, it's been 15-30f outside during my testing, have not had an energy audit but my house is fairly "tight", I lose 1 degree per hour in the summer or winter if HVAC is turned off regardless of ambient conditions, I wonder if 75,000 BTU is undersized? The house was originally constructed as a bilevel with an unfinished basement... 1000sq/ft upper level and now 1000sq/ft lower level (they just cut into the existing ducting to provide for the basement).... maybe need a larger unit now?
Old 12-19-2009, 01:17 PM   #4
Hvac Pro
yuri's Avatar
The only accurate way to know is to do a heat load/loss calculator:Load Calculator
Gaining 8F /hr sounds good to me so I don't think it is undersized. Sometimes we wish we burned less gas but it may be normal.
Old 12-19-2009, 01:22 PM   #5
roughly
Heat loss is X BTU/[(sq.-ft)-HDD], with X ranging from 1.7 for a tight house to 11, with avg. = 6.
For 2000 sq. ft. you'd have avg. 12,000 BTU/HDD.
For 1000 HDD in a month, your avg. loss is 12 MBTU, or 17,000 BTU/hr.
http://www.degreedays.net/
4 ccfs = ~400,000 BTU in 24 hrs. = 17,000 BTU/hr. Do you have 1000 HDD in a month?
At 75,000 BTU/hr your [single stage?] furnace is on 22% of the time.
Old 12-19-2009, 02:54 PM   #6
An old Tradesmen
Rewards Points: 7,376
If it was undersized. It wouldn't be raising the house temp 8 in an hour.
Old 12-20-2009, 08:25 PM   #7
Confirming a right sized single stage furnace for your house and climate
Find your Outside Design Temperature (ODT) from the link
http://www.hrt.msu.edu/energy/Notebo...by_AJ_Both.pdf
calculate the A factor
A = (65-ODT)/(-100)
then calculate your expected furnace Duty Cycle
in percent
DC = 100(on time)/(off time + on time)
at your outside temperature T
Then,
DC = (T-65)/A
and
T =( DC)(A) + 65
The Outside Design Temperature from the link for Portland, Maine is -6F
Then, A = -0.71
then
T...... DC
65.0F..0%
-6.0F 100%
20F ..63%
and
DC ...T
100% -6F
0% ..65F
30% 43.7F
If you measure your duty cycle over one or two cycles
(should take a few minutes)
and record the outside night time temperature
corresponding to this Duty Cycle,
over several days of varying night time weather,
the average of these readings should be
within a few percent of the predicted values.
Old 12-20-2009, 10:24 PM   #8
An old Tradesmen
You would need to know the actual output of the furnace.
Old 12-21-2009, 05:00 AM   #9
Your home in only need 37,500btu.
75,000 is over sized but seems to be the standard form homes 900 to to 1600 sq ft.
hvaclover is offline   Reply With Quote
Old 12-21-2009, 02:16 PM   #10
It would seem so, but I don't think it's necessary for this calc.
The single stage furnace is just some "heat machine" that needs to be on
all the time at -6F and
off at 65F, and
on half the time at
T =( 50)(-0.71) + 65 = 29.5F.
This does assume a straight line relationship between furnace output and duty cycle and temperature, so the "on time" should maybe be 10 minutes or more for this to be true.
I asked Bryant about this and they gave me the runaround.
I did a more complicated spreadsheet that should work with multi- or single-stage furnaces, using only input BTUs/hr, based on my January '09 gas bill.
It tells me that my 169K furnace should have been a 69K unit. It's typically on 1/4th of the time, with on times of 6 minutes. ODT to the 99% level = +14F, 3100 sq. ft. including a 900 sq. ft. basement.
Can't get unit to turn on need electrical help please-wiring diagram included igotshocked Electrical 33 01-30-2014 05:13 AM
Ruud Pack unit "KABOOMS" upon First Light Up of the Day! Wirenut2tite HVAC 18 12-15-2012 10:11 AM
Heil 5000 HE unit not working oldtom HVAC 2 09-27-2009 07:27 PM
Heil HVAC unit fan won't go on help! rivera76 HVAC 12 08-29-2009 08:25 PM
AC condensing unit failure? Hotinsummer HVAC 3 08-09-2009 02:08 PM