Old 07-01-2013, 12:54 PM   #46
Hvac Pro
yuri's Avatar
Rewards Points: 150
I did not say the system will last or even work properly and I stated that many posts ago on the original thread when we discussed the 8 SEER coil with a 10 SEER condenser. complete waste of good time and $$ IMO but our poster has limited $$ and wants to try cobble it together for awhile. not my choice. my point is we did not have or use micron gauges until R410 came out as moisture was not destroying systems or on the manufacturers radar. pure low temp refrig is different but that is not the same as AC. putting a new larger filter drier in will compensate for any small amount of moisture and how long do we really expect this cobbled together system to last. the Pros know better. Glad to hear the ole guy is still kickin.
Old 07-01-2013, 06:22 PM   #47
It's cooling the house very well,
quickly, & cycles.
I'm very pleased & hope I can enhance the longevity of the system.
I'm interested in having the system adjusted & balanced, as well as the installed components will allow.
I'm planning to ask an Installer/Tech to check the "Sub cooling and Super heat readings along with the unit amp-draw".
What is the range for each of these specifications, or where should I be able to find them?
What else should I have checked (I mean, what else on the A/C)?
Thanks Again,
Uni
Unicornz0 is offline   Reply With Quote
Old 07-01-2013, 06:26 PM   #48
An old Tradesmen
Rewards Points: 7,816
Do you have a TXV, or fixed metering device.
Old 07-01-2013, 06:41 PM   #49
Hi BeenThere,
I was told it's an orifice, 3/8" x 3/4".
Thanks,
Uni
Old 07-01-2013, 10:30 PM   #50
An old Tradesmen
Indoor wetbulb needs checked to know what the SH should be. SC should not be more then 10 degrees higher at the most.
Old 07-01-2013, 11:01 PM   #51
Please explain what you have written.
What should all of the specifications be you have previously asked about?
What is "indoor wetbulb"?
Old 07-01-2013, 11:41 PM   #52
Should I be concerned about the superheat, since my system has an orifice, but not a TXV valve?
Should I be concerned about the subcooling, & the unit amp-draw?
I'm trying to have my system run as well as the installed components will allow.
Please advise.
Thanks In Advance,
Uni
Old 07-02-2013, 04:48 AM   #53
An old Tradesmen
The lowest temp that moisture will evaporate at. It along with the outdoor temp are need to determine target SH.
Amp draw is not specific. It will vary by the conditions of the day. it should be less then then RLA listed on the data tag.
Since you have a piston, the Carrier SC chart does not apply.
Old 07-02-2013, 06:57 AM   #54
Thank you BeenThere.
Which piston are you referring to?
There is an orifice.
How should SC be determined?
Old 07-02-2013, 04:06 PM   #55
An old Tradesmen
The indoor metering device. Orifice or piston, is a fixed metering device. SC can not be targeted for it. Only SH.
Old 07-02-2013, 04:11 PM   #56
Thanks.
What should super cooling be compared to, to insure super cooling is at the correct level?
Old 07-02-2013, 04:31 PM   #57
An old Tradesmen
SC/Subcooling should be within 10 degrees of teh superheat after the indoor temp is near set point.
Old 07-02-2013, 05:22 PM   #58
Thank you.
In this particular situation how then can sub cooling be calculated, & compared against super heat?
Please explain in detail.
Old 07-02-2013, 05:27 PM   #59
An old Tradesmen
Thank you.
When the indoor temp is near the set point temp. take a wetbulb reading. Check outdoor air temp entering the condense. use a superheat slide chart and determine what the super heat should be. if the super heat is near that amount. Then the subcooling should be within 10 degrees of that.
Old 07-03-2013, 01:01 AM   #60
HVAC condenser not wired properly? LynnX HVAC 9 01-24-2014 08:40 PM
A/C Condenser Disconnect Box whattodo Electrical 18 03-22-2013 09:45 AM
Proper trunk/duct size? gjones HVAC 7 12-06-2011 07:18 PM
A/C condenser circuit size Rustygaff Electrical 23 10-30-2011 07:15 PM
Building a patio cover...span and size of lumber Q's jongordo8 Building & Construction 1 08-30-2009 12:08 AM