Please help ac outside unit not running..
Our thermostat comes on, the air handler blows, but the outside unit does not come on. We tested the capacitor, its fine. We replaced the single. Pole contactors with a double pole, everything seems to test fine but the fan and compressor don't come on. When we manually override the contactor it will run but blows hot air inside.
jonhaddigan is offline   Reply With Quote
Old 05-14-2016, 01:33 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 1,412
Re: Please help ac outside unit not running..
Is it a heat pump?
Post brand and model #.
Do you have 24 volts AC at the contactor coil?
If it is a heatpump and you press the contactor in and the reversing valve is in heat mode you will get heat. Need to see if the thermostat is sending 24 volts on the Y wire to the outdoor unit and contactor. Check between Y and C out there or at the furnace.
Old 05-14-2016, 02:37 PM   #3
Rewards Points: 6
It's a Trane split system 2TWB
Old 05-14-2016, 02:39 PM   #4
Rewards Points: 6
Getting 24 volts at the coil. When manually pushing in the contactor heat comes out
Old 05-14-2016, 02:58 PM   #5
Hvac Pro
yuri's Avatar
It looks like a heat pump which I don't see many of where I am.
If you are getting 24 volts across the coil it should pull in unless the contactor is sticking. Need to check across the coil and NOT to ground or you can get fooled.
However the reversing valve should be in the cooling position as it gets a signal at the same time to move it to cool ( unless it is a brand that does not, Rheem I believe ). If it is getting the signal and you push the contactor in it should cool.
Check back here later as there may be some techs here who know that unit better.
Old 05-14-2016, 02:59 PM   #6
Rewards Points: 6
Thank you
Old 05-14-2016, 03:02 PM   #7
Hvac Pro
yuri's Avatar
Yur Welcome.
My comrade Beenthere knows Trane and there will be others here within 8 hours or tomorrow.
Old 05-14-2016, 03:13 PM   #8
Rewards Points: 3,658
What's the voltage across the coil?
roughneck is online now   Reply With Quote
Old 05-14-2016, 05:01 PM   #9
Rewards Points: 6
24 volts
Old 05-14-2016, 06:27 PM   #10
Rewards Points: 46
If there is 24v across the coil of the contactor, and it's not pulled in, then it's dead. Replace it.
Cheers!
supers05 is offline   Reply With Quote
Old 05-15-2016, 11:34 AM   #11
Rewards Points: 6
I replaced the contactor and still same issues. Is it possible the contactor is faulty or can something else cause this?
Old 05-15-2016, 11:52 AM   #12
Rewards Points: 244
Are you measuring 24 volts at the contactor or at the connections coming into the condenser? The contactor you purchased has a 24 volt coil?
BayouRunner is online now   Reply With Quote
Old 05-15-2016, 11:55 AM   #13
Rewards Points: 6
At the contactor is 24 volts and the coil is a 24 volt coil.
Old 05-15-2016, 12:09 PM   #14
Rewards Points: 244
if it has 24 volts at contactor and is not pulling in then the contactor is faulty. I find the odds of having your old contactor and new contactor bad are not too likely though. You mentioned earlier when you engaged contactor unit was producing heat. So I am assuming you are getting 220 volts. It's hard to tell over the internet but I have to ask so I can understand. When you are measuring 24 volts, you are measuring with a lead on each side of coil and not to ground right?
Old 05-15-2016, 12:14 PM   #15
Rewards Points: 6
220 coming in but 24 at ground.
Tags
compacitor , contactor , hvac , trane
Can't get unit to turn on need electrical help please-wiring diagram included igotshocked Electrical 33 01-30-2014 06:13 AM
Air Handler is running but outside unit is not Drewske44 HVAC 5 12-07-2013 09:23 AM
Outside Unit Not Running chris1381 HVAC 3 08-24-2010 07:22 AM
compresser unit running ok, try's to restart Pat33019 HVAC 2 09-26-2009 12:44 AM
Furnace leak while running AC unit lbartowski HVAC 3 09-18-2009 02:46 PM