Pilot Wont Stay Lite - HVAC - DIY Chatroom Home Improvement Forum
Old 11-12-2012, 02:41 PM   #1
pilot wont stay lite
ok i have a standing pilot gas valve and the furnace will run a cycle and shut down. then after the blower shuts off i hear a click frm the gas valve and the pilot goes out is my gas valve bad replaced thermocouple still doing it
bigden67 is offline   Reply With Quote
Old 11-12-2012, 02:46 PM   #2
I'm Your Huckleberry
Rewards Points: 2,270
You'd need a manometer to test (gas) pressure through the gas valve.
Thanks.
Doc Holliday is offline   Reply With Quote
Old 11-12-2012, 02:53 PM   #3
were would i get the meter thans
Old 11-12-2012, 03:02 PM   #4
Hvac supply house but not sure they'll sell to the public. Could try Grainger or online.
Digital manometer.
This is what I use, you might find one cheaper.
Have you tried simply thumping the gas valve?
Thanks.
Old 11-12-2012, 03:04 PM   #5
Have you checked the wires to the valve, make sure the connections are solid? A gas valve usually only clicks once as it receives voltage to open. If there were a loose wire then the voltage could be interrupted.
Thanks.
Old 11-12-2012, 03:11 PM   #6
yes try the thump and checked wires.is that meter the one that checks in w.c and no supply houses wont sell to public. thanks
Old 11-12-2012, 03:17 PM   #7
yes, inches in water columns.
Thanks.
Old 11-12-2012, 03:21 PM   #8
ok thank u for ur help
Old 11-12-2012, 03:32 PM   #9
Why does he need a manometer? Pilots will stay lit under the most severe cases of low press.
Standing pilots use a magnetic operator that is held in by the DC millivoltage the thermocouple produces. Either the pilot is partially plugged causing poor pilot impingement or the magnetic operator is weak.
The pilot flame should envelope the top 1/4 of the thermocouple and should be a steady non-wavering blue in color flame.
hvac5646 is offline   Reply With Quote
The Following User Says Thank You to hvac5646 For This Useful Post:
ben's plumbing (11-12-2012)
Old 11-12-2012, 06:51 PM   #10
Rewards Points: 196
Sounds like dirty pilot orfice, causing burner to suck pilot flame out when it shuts off.
HVACTECH96 is offline   Reply With Quote
The Following User Says Thank You to HVACTECH96 For This Useful Post:
Old 11-12-2012, 07:06 PM   #11
Rewards Points: 582
yep start with addressing the pilot itself...see how strong it is ...make sure it is fully engulfing thermocupler.....ben sr
Old 11-12-2012, 07:43 PM   #12
Watch the pilot flame when the burners shut off. It's not uncommon for a cracked heat exchanger to let air blow the pilot around and cause the safety to kill the gas. And by not uncommon I mean 99 out of 100 times that's the root cause of the problem.
Old 11-12-2012, 08:08 PM   #13
how
Rewards Points: 1,070
Make sure the pilot flame is enveloping the end of the thermocoupler by either repositioning the thermocouper in the pilot assy sleeve, cleaning or replacing the pilot orifice or by adjusting the pilot gas pressure. Also make sure there are no flames occuring at the bottom of the pilot assy which can heat the cold junction of the pilot.
Watch the pilot flames position to see if the pilot flame moves away from enveloping the thermocoupler during any part of the entire heating cycle.
Let us know what happens.
You can use any thermocoupler adapter in between the valve and the thermocoupler which allows you to use a standard meter to measure the dcmv strength of the thermocoupler and the dcmv pilot electromagnet threashold drop out point of the gas valve.
The only loose wires that would normally knock out a pilot light would be if you had a powerpile system. The coupler needs only to be finger tightened plus a 1/4 turn by wrench.
how is offline   Reply With Quote
The Following User Says Thank You to how For This Useful Post:
Old 11-12-2012, 08:50 PM   #14
That number is pretty high. That's like saying 99% of all standing pilot furnaces had ht ex cracks from the factory.
The Following 2 Users Say Thank You to hvac5646 For This Useful Post:
ben's plumbing (11-12-2012), how (11-12-2012)
Old 11-12-2012, 09:03 PM   #15
how
In my career it's been closer to one percent but most of my clients are regulars so annual exchanger checks seldom let a crack advance far enough to effect the pilot.
Whirlpool 50G Gas Pilot Won't Stay On Dowhatican Plumbing 1 10-29-2012 04:17 PM
pilot lite will not stay lit Gary Cornell Plumbing 1 03-03-2012 03:06 PM
Pilot on Williams millivolt wall heater goes out every 8 to 16 hours wornways HVAC 30 06-22-2011 04:29 PM
Pilot light does not stay on cprao HVAC 11 02-14-2010 06:38 PM
Is a pilot light supose to stay on? simonb HVAC 2 06-11-2008 06:16 PM
