Payne Pg9maa Trouble - HVAC - DIY Chatroom Home Improvement Forum
Old 10-30-2011, 03:56 PM   #1
Payne pg9maa trouble
I have a payne pg9maa furnace with an issue. When you call for heat, the inducer motor runs thru it's sequence. the igniter glows. the the gas valve opens. I see a blue flame for a few seconds, then I hear a buzz and the flame shuts off and system powers down. It will keep cycling thru this process without locking out. Also, it does not flash a trouble code. So far I have cleaned the filters, cleaned the condensate trap, cleaned the flame sensor, and replaced the pressure switch. Anyone have any ideas?
baerlili2 is offline   Reply With Quote
Old 10-30-2011, 07:52 PM   #2
Rewards Points: 492
Check for any obstructions to air exhaust and input, usually PVC pipe outside.
If you cleaned flame sensor with sandpaper, you may have ruined it. They are one of the cheap parts to replace. I'd try that.
diyorpay is offline   Reply With Quote
Old 10-30-2011, 08:05 PM   #3
Thanks, I used 000 steel wool on the flame sensor. It doesn't have any scratches or pitting. I will check the exaust. It is on it's third board. If the board is bad could it act this way? Also, what about the gas valve?
Old 10-30-2011, 08:21 PM   #4
Rewards Points: 492
Check that hose from the inducer draft fan to the pressure switch for any cracks etc, especially at each end. If bad and it's long enough, cut small piece from end and refit.
Old 10-30-2011, 09:14 PM   #5
how
Rewards Points: 1,102
Its interesting that you are not getting any fault code.
A faulty thermostat can cause repeated short cycling that will not give a fault code.
Bypassing the thermostat at the furnace is a worthy test to try.
Repeated board failures also warrants a double checking of all grounds related to the furnace, right back through the electrical shut off & box to the house service.
Although I've questioned this convenient manufactures defence & excuse for repeated board failures, I've also often found poor grounding on those same problem systems.
how is online now   Reply With Quote
Old 10-31-2011, 08:43 PM   #6
thanks to all who replied. I replaced the thermostat and that seems to do the trick. Thanks again
Payne Furnance PG9MAA problem peng teo HVAC 34 01-14-2012 04:13 AM
Payne Heat Pump Traouble ATC HVAC 15 07-23-2011 08:15 AM
Payne gas furnace - blower fan running continuously Ed40 HVAC 0 02-05-2011 03:19 PM
Payne Furnaces mick6311 HVAC 1 06-26-2007 10:10 PM
new 3 ton hvac Payne units. No cool air comes out when fan, compressor,thermostat run runbikeengr HVAC 10 04-10-2007 06:59 PM