Payne Heat Pump Trouble
I have a 4 ton Payne heat pump. The problem I am having is the a/c be running and blowing cold, then it will switch and start blowing hot air out of the vents. The outside units appears to be going into defrost mode. I have changed the thermostat thinking it was bad. That did not solve the problem. I will turn everything off for a while then back on and the a/c will work for a while. Any suggestions on where to start.
ATC is offline   Reply With Quote
Old 06-05-2010, 06:26 PM   #2
fabrk8r
fabrk8r's Avatar
Sounds like symptoms of a reversing valve going bad. My advice is to call an HVAC tech to check your system.
"The physician can bury his mistakes, but the architect can only advise his clients to plant vines." -- Frank Lloyd Wright
fabrk8r is offline   Reply With Quote
Old 06-05-2010, 06:49 PM   #3
ATC
Old 06-05-2010, 09:14 PM   #4
Try this:
turn off power to the a/c condenser
pull the cover off the side of the unit with the electrical connections
what color wires are where on the low voltage side? (ie red goes to R brown goes to C)
or, take a picture and post it. We'll go from there.
You may also have a bad controller board, defective defrost switch, or damaged LV wiring.
When it switches to defrost mode, what does it do exactly?
fpeftw is offline   Reply With Quote
Old 06-06-2010, 06:41 AM   #5
ATC
Update: No Condenser Fan
When the system starts blowing heat out of the vents the outside unit fan stops running. I may be wrong on the unit going into defrost mode. Would the condenser fan casuse this issue.
THANKS
Old 06-06-2010, 11:00 AM   #6
You can still hear the compressor running after the fan stops turning?
Old 06-06-2010, 11:06 AM   #7
An old Tradesmen
Rewards Points: 8,176
Probably a bad defrost sensor.
Disconnect the defrost sensor. And see if that stops it.
Old 06-06-2010, 11:51 AM   #8
ATC
Yes, the compressor still runs after the fan shuts off. The inside unit is still running but blowing hot air. The air temperature from the vents is around 100-110 degrees. When the a/c is working the air temperature is around 60 - 65 degrees.
Old 06-06-2010, 12:43 PM   #9
An old Tradesmen
Follow the instructions in post 7. And you'll find out in a little while if its your defrost board, or your defrost sensor.
Old 06-06-2010, 09:04 PM   #10
Of course you know where the defrost sensor hooks into the board, right?
Old 06-07-2010, 07:13 PM   #11
ATC
Thanks for the help. I replaced the defrost board. Everything was working fine for a few hours then the compressor shuts off, but the condenser fan was still running. Now the air blowing out of the vents was only 90-95 degrees. I reset all the breakers and restarted the system. The compressor is now running. Any suggestions on what could be causing this.
Old 06-07-2010, 09:33 PM   #12
An old Tradesmen
Are you sure you didn't miswire the board. And have the compressor contactor connected tot eh fan terminals.
Did you test the defrost stat?
Old 06-08-2010, 08:53 AM   #13
ATC
It was wired correctly. It seems that the defrost thermostat is bad. I unplugged the defrost thermostat from the board and the system works like it should. I will replace the thermostat and go from there.
Old 06-08-2010, 01:31 PM   #14
An old Tradesmen
So you didn't do the test like I said in post 7, before you went out an bought a defrost board.
Oh well. They're cheap.
Old 07-23-2011, 12:21 AM   #15
i am having the same problem as this person with the payne system blowing out hot air ....exact same problem...help, its 105 degrees outside and we have to shut the system off due to the fact it is trying to fry us in our sleep.....
rosewalton is offline   Reply With Quote
Comparison and Heat Pump Selection help... ChrisDIY HVAC 7 03-06-2010 08:34 PM
New Heat Pump..questions? ddave23 HVAC 4 03-05-2010 05:13 AM
What temp does my Heat Pump stop producing good heat or what is the threshold? twilightcall HVAC 15 02-12-2010 09:46 PM
Heat pump thermostat emergency switch joe913 HVAC 2 12-10-2009 12:54 PM
Brand new Carrier Infinity 16 Heat Pump Stopped Working I think needmyac HVAC 3 07-07-2009 06:12 PM