-   -   payne furnace prob (http://www.diychatroom.com/f17/payne-furnace-prob-94132/)
drisco 01-31-2011 07:06 PM
payne furnace prob
after turning on the heat the furnace combustion box overheats causing manual limit switch to go off . i have the heat set to 66 degree however it only gets to 58 degrees. the furnace exhaust gets a natural gas smell outside. the furnace gives code 33, and blower motor runs until i reset furnace it was installed 97
i replaced cleaned
cleaned intake and exhaust pipe
thermostat
air filter
replaced burned out draft inducer
last yr replaced flame sensor and flame ign.
payne furnace model #490aav036060
kenmac 01-31-2011 07:16 PM
not getting enough air flow across the HX .dirty coil. closed off vents , not enough return air
drisco 01-31-2011 07:22 PM
i cleaned the coil
drisco 01-31-2011 07:23 PM
all vents open air comes out
kenmac 01-31-2011 07:26 PM
Is this 1 of the small limits that you reset by pushing a small button. If so it's a roll out limit & you need to have the H X or vent system checked
drisco 01-31-2011 07:31 PM
yes it is one of the small ones u push in did and over heated ? could u be limit switch on fire wall
kenmac 01-31-2011 07:33 PM
Can't make out what this means. You need to have a PRO check your unit
drisco 01-31-2011 07:55 PM
. [IMG]file:///C:/DOCUME%7E1/owner/LOCALS%7E1/Temp/moz-screenshot.png[/IMG][IMG]file:///C:/DOCUME%7E1/owner/LOCALS%7E1/Temp/moz-screenshot-1.png[/IMG]one of my friends thought that the Heat exchangers, are sooted and or limit switch on fire wall behind draft inducer is at falt
HvacWiz 01-31-2011 09:17 PM
Your secondary heat exchanger is plugged up.