Packaged A/C 2 Wire Thermostat Wiring - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 04-03-2012, 08:02 PM   #16
I'm Your Huckleberry
Rewards Points: 2,270
You need to check to see if it has 240 across both legs. Check at the bottom terminals of the contactor, where the power first comes in.
Thanks.
Doc Holliday is offline   Reply With Quote
Old 04-03-2012, 08:03 PM   #17
And no, there is no waiting for the unit to come on if the contactor is in. Did you push it in far enough?
Thanks.
Old 04-03-2012, 08:31 PM   #18
It didn't go far, maybe 1/4 an inch, a little more. The panel is still open, I will go try again. As to the volts, I have to wait, blew one of the fuses and burned one of the leads on the meter yesterday being stupid, have to go to radioshack tomorrow afternoon.
nednerb is offline   Reply With Quote
Old 04-03-2012, 08:37 PM   #19
It is clearly making contact, but no good. More tomorrow.
Old 04-04-2012, 04:20 PM   #20
Alright, here is an update. I got new leads for my meter and it works great. I tested everything I could and here is what I have found. I discovered 120v at all locations from the breaker to the cut off box to the control box contents. Almost every single connection on everything in the control box yielded 120v when touching ground. All the connections on both capacitors and the contactor yielded 120v. The transformer has 120v present on the leads on top and 8.6v coming out of the bottom. My question is: how do I test for the full 240? Everywhere I check I have to have one lead touching ground, the second lead can only contact one place at a time, always yielding 120v. You said to test it 'across both legs', if I connect both leads to both hot wires coming from the breaker there is no ground to complete the circuit so the meter says 0, please tell me what I am missing. Thanks!
Old 04-04-2012, 04:32 PM   #21
If you do not have 240-ish combined total high voltage across both legs than something is wrong with your high voltage, with one leg or the other. I'd start with the breaker. I just went outside, this is on my own condenser.
Thanks.
Old 04-04-2012, 04:35 PM   #22
So all I have to do is put a lead to each terminal on the breaker and I should get 240?
Old 04-04-2012, 04:36 PM   #23
An old Tradesmen
Rewards Points: 7,794
To check for 240 volts, you check across both hots. You don't check for one hot to ground.
The Following User Says Thank You to beenthere For This Useful Post:
Doc Holliday (04-04-2012)
Old 04-04-2012, 04:37 PM   #24
Yes, correct.
Thanks.
Old 04-04-2012, 04:40 PM   #25
SUCCESS!!! I turned the main off and shifted the breaker to another spot on the panel, flipped it back on and voila! The a/c turned right on with some excellent cold air! I will put everything back together, if I have problems with my thermostat I will let you know. Thanks so much for your help, I appreciate it so much!!!
Old 04-04-2012, 04:46 PM   #26
I've got one of those old FPE fire starting panels at my place, knock on wood. The voltages fluctuate all over the grid at the breaker.
Thanks.
Old 04-04-2012, 04:47 PM   #27
Good deal. Sometimes all it takes is a reset.
Thanks.
Old 04-04-2012, 05:42 PM   #28
The thermostat works great too, its done, thanks so much.
Tags
2 wire , package unit , thermostat , trailer
connecting a 4 wire SP thermostat to a 2 wire system wiichkin Electrical 4 08-15-2010 01:35 PM
Thermostat to Controller Wiring Molson HVAC 1 07-05-2010 06:24 PM
Adding ground in old home ChaosTheory Electrical 6 06-16-2010 04:02 PM
Wiring on Hunter Analog Thermostat woomama HVAC 16 03-22-2010 01:52 PM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 09:41 PM