Outside AC Unit Not Working - HVAC - DIY Chatroom Home Improvement Forum
Old 08-29-2014, 10:39 AM   #1
Outside AC unit not working
My house started getting really hot, so of course I checked the thermostat. Was set to 71 while actual temp was 81. There is air blowing out of the vents, but not cold air. I went outside and checked the outside unit and the fan was not spinning. I put my ear to it and there is a very slight humming, telling me there is power. At first I thought capacitor, but the stick test did not get the fan blades moving. Any ideas? Thanks!!
Jreo97 is offline   Reply With Quote
Old 08-29-2014, 11:29 AM   #2
Rewards Points: 380
humming could be contactor coil being energized, but breaker could be blown. check for 240 to outdoor unit and 24 volts to contactor coil, are you capable of checking for power with a meter?
HVACDave is offline   Reply With Quote
Old 08-29-2014, 12:26 PM   #3
Thanks for your reply HVACDave! I know the main circuit breaker (in my main electrical panel) is OK because it is not tripped (already checked that), but there are a couple of fuses in it's own separate box mounted on the outside of the house by the AC unit. Is it possible these are blown and the 240 isn't getting to the outdoor unit? I didn't really think it would be a blown fuse due to the slight humming, but your post makes me think differently now.
Old 08-29-2014, 11:24 PM   #4
I'm Your Huckleberry
Rewards Points: 2,270
capacitor. is the compressor running while the fan is not? ice forming along refrigerant line mainly the bigger one that is insulated?
if nothing is coming on outside, compressor and fan than it's either a capacitor and/or high voltage, breaker. Mind you a breaker can appear to be "on" but may need to be reset regardless.
low voltage from inside at furnace.air handler is what powers the contactor thus the humming from contactor.
open service panel and look at capacitor, if it's bulged on top or jelly type substance is seeping from it it's bad.
Thanks.
Doc Holliday is offline   Reply With Quote
Old 08-31-2014, 01:05 PM   #5
Thanks for the reply guys! I changed the fuses on the outside and the outside fan works again!! However it's making a weird surge sound every 30 secs or so.. Is that normal?
Old 08-31-2014, 03:04 PM   #6
Rewards Points: 3,256
Is it cooling your house now? There is a reason that your fuse(s) blew and you should get someone to check it out unless you want to dig into it yourself. Bad compressor or maybe capacitor comes to mind if the unit isn't cooling.
zappa is offline   Reply With Quote
Old 08-31-2014, 05:27 PM   #7
Fan is running and air is cool now coming out of vents after 30 amp fuses were changed on outside fuse box (for AC only) but that surge noise happens every 30 secs.. Even though it works, I decided to leave it off because of that sound. Does that sound soud familiar to you? Almost sounds like just before a transformer blows
Old 08-31-2014, 05:59 PM   #8
Quick update, I took off the service panel and took a look. The capacitor look ok as it's not puffed out. However, that surge sound i mentioned is electrical arcing. There are burnt wires on the relays. Possible bad relays? Or signs of a much bigger problem?Thanks!
Old 08-31-2014, 06:23 PM   #9
Hard to say....arcing and burnt relays still shouldn't blow the fuses unless it's so destroyed that there is a short circuit between the phases or to ground. Wires, internal capacitor short to case, compressor and fan motor windings are also suspect.
Trane Pkg unit Blower Motor not working clw1963 HVAC 16 07-09-2014 05:17 PM
King make up air unit RWolff Electrical 3 04-23-2013 10:22 PM
Bryant AC unit not working emcinnis HVAC 8 08-18-2011 10:12 PM
Heil 5000 HE unit not working oldtom HVAC 2 09-27-2009 07:27 PM
AC condensing unit failure? Hotinsummer HVAC 3 08-09-2009 02:08 PM