-   -   Only 4 of 5 burners light on my furnace (http://www.diychatroom.com/f17/only-4-5-burners-light-my-furnace-159281/)
Chris66204 10-07-2012 01:24 PM
I have a 12 year old Comfortmaker gas furnace.
It operated fine all last winter.
When I went to fire it up the first time today, only 4 of the 5 burners light off (burners 2 thru 5 when counting from where the gas enters the manifold).
The ignitor is in front of burner 5, the ignition sensor is in front of burner 1.
Because burner 1 never lights, there is no ignition feedback and after 15 or 20 seconds the gas valve closes. It will retry about 4 times before going into a soft lockout because of the failed ignition.
I don't see any obvious blocakges in the burner nozzles.
Any thoughts on how to proceed?
JJboy 10-07-2012 01:48 PM
Check the gas pressure and clean the burners.
biggles 10-07-2012 01:51 PM
you said burner nozzle but what about the manifld fitting that feed that #1 buners track..pop out the burner spider or bug is blocking the gas into it...box end wrench soft tap loosen it,and finger tight back in with a tweek from the box wrench to tighten it...mine as well check them all ...wire brush the ignition track along the burners...except for 1 and 5 all others are the same when you pull them out
how 10-07-2012 01:52 PM
Usually a bit of debris in the crossover between the burners that are burning and the one that is not.
Chris66204 10-07-2012 03:05 PM
Update -
I pulled the burner manifold fitting and verified it was clean.
I also adjusted the pressure and no joy.
I'm thinking there is something to How's response - I can see the flame on the crossover between all the other burners but it is non-existent between burner 2 and burner 1.
I'm going to try and clean that up, but if you have any specific things to look for there, please let me know.
how 10-07-2012 03:26 PM
Pull the burner that isn't lighting and the one beside it that is. Look for a thin slot on eitherside of the burners that allows the burner flame to travel from one to the next.. A metal strip from a tin can is thin enough to use as a tool to clear out any debris. If you are unable to remove the burners, you can bend your metal tool into a "U" and still may be able to clear them.
hvactech126 10-07-2012 04:48 PM
pull and clean ALL the burners
beenthere 10-07-2012 06:27 PM
So what pressure do you now have it set to? You did use a manometer to adjust it right.
ben's plumbing 10-07-2012 06:34 PM
yes pull entire burnner assy and clean them all....also as beenthere said what did you set manifold pressure to and with what...ben sr
Chris66204 10-07-2012 07:01 PM
Pulled the burner assembly and cleaned the crossover assemblies. Started up just fine after that. Thanks for all the help.