oil furnace will not light
My oil furnace will come on then shut off 30 sec later. so I changed the oil filter and it was dirty be still same thing I have to press the reset button then it shuts down . so what do you guys think could be the problem ?
Jerrystrauss is offline   Reply With Quote
Old 01-05-2012, 08:15 PM   #2
An old Tradesmen
Rewards Points: 6,116
When is the last time it had a good clean and tune. probably has a bad nozzle. Or it could be the ignition transformer, or even the oil pump, plus a few other things.
Old 01-05-2012, 09:32 PM   #3
I know the pump is working and I don't know when or if it was cleaned I bought the house in June and this is the first time I have turn the heat on since the home inspection. I had a new condenser unit put in over the summer but not the inside unit so that shouldn't have changed any thing. how can I test the unit to see what might be wrong?
Old 01-05-2012, 09:35 PM   #4
An old Tradesmen
Remove jet line from draw assembly, and point it into a container, then run burner and see if oil comes out.
If so, pump is working. If not, either pump is not working, or air is in line, or you are out of oil, or pump coupling is bad.
Old 01-05-2012, 09:38 PM   #5
Rewards Points: 582
just a follow up to beenthere...have it serviced by good company to get it ready for the season and mention these things to the tech then you know its safe and done right.. no disrespect to you but oil can be trickey to work on....ben
Old 01-05-2012, 10:38 PM   #6
REP
Ok a short list of possibles.
A dirty nozzle.
Cracked poecilin/s or worn out electrodes.
Water in fuel
Weak transformer.
bad relay .
dirty flame sensor.
weak pump.
loose flare connection.
bad air setting
plus probably 6 other things.
With a professional clean and check will cost 2-3 hundred dollars and if set up with instraments (an absolute must)
If this is done by a good tech then you will possibly save around $400.
REP is offline   Reply With Quote
The Following User Says Thank You to REP For This Useful Post:
ben's plumbing (01-05-2012)
Old 01-06-2012, 12:00 AM   #7
cad cell
im a gas tech but been around the dirty oil, 99% its the cad cell , its like a flame sensor for a gas furnace, if the sequence of operation is ok untill the burner lights, then its the cad cell not telling the main valve that there is a flame and to shut down, you can try to clean it, but good chance its going to need a replace, cheers Legacy
Legacyairsystem is offline   Reply With Quote
Old 01-06-2012, 07:02 AM   #8
Rewards Points: 1,214
When you change the filter you must fill the filter housing with clean oil and remove the line off the pump (as been said) and direct it into a container until all the air is out of the line the hook it back up and restart it. Don't be pushing that RED button more than once or twice or you could have a major problem.
COLDIRON is offline   Reply With Quote
Furnace pilot light will not ignite - Carrier 58 GS Furnace? rasilun HVAC 3 10-29-2011 10:38 PM
Furnace will light - if I hit it! Chuch HVAC 1 10-28-2011 03:05 PM
Bryant furnace won't light, not HSI amylynn6 HVAC 8 11-01-2010 11:07 AM
Weathermaker 8000 gas furnace will not light karyn HVAC 1 01-24-2010 12:17 PM
Carrier Furnace Series 160 Pilot Light issue eastons HVAC 2 03-15-2009 03:26 PM