-   -   Oil Furnace Emergency shut off switch location? (http://www.diychatroom.com/f17/oil-furnace-emergency-shut-off-switch-location-148415/)
LarryNH914 06-27-2012 10:24 AM
Hi, I am redoing a stair to come up to code at my Gal's house. We are switching the stair direction, and there is a Furnace switch that I am questioning the location of.
History of the house: This house used to have a full basement with stairs down to the basement where the Furnace Emergency Shut off switch was located at the top. The house was moved to it's current location for road widening. The basement was replaced by a crawl space. The stairs to the basement became a closet (where the emergency switch still resides) and access to the crawl space is from a bulkhead outside the house.
So, the current situation is that the Emergency Furnace shut off switch is in a closet in the first floor. There is no switch in the crawlspace.
I have not found real good information on where the Furnace Emergency shut off switch should be located. The best I can guestimate from what I read so far is that a better location would be inside the entrance of the crawl space in sight of the furnace.
Additionally, access to the fuse box is near the first floor entrance, where a clearly marked furnace breaker is located.
The reason for this would be:
1) It can be used by service personal to shut off power when servicing.
2) The furnace could be shut off easily from the circuit panel from the first floor.
3) The current location (within 10 feet of the circuit panel) will be out of the closet due to the remodel(first thought was that I put it in a recessed box to prevent accidental switching on/off)
So.... The question is, where should a Oil Furnace emergency shut off switch be located for a furnace located in a crawl space with access to the space from outside? Does anyone know the code (or at least common sense?)
beenthere 06-27-2012 04:06 PM
At the entrance to the crawlspace.
Its suppose to be outside of the entrance, by code.
stickboy1375 06-27-2012 05:15 PM
12 Attachment(s)
What if you have two entrances?
beenthere 06-27-2012 05:38 PM
Then the one most commonly used. if both are used equally, then the one closest to the furnace. If they are both equally close to the furnace, then which ever one you want.
stickboy1375 06-27-2012 05:39 PM
12 Attachment(s)
Is that code or opinion? I'd like to see the actual code on a remote switch location.
beenthere 06-27-2012 05:44 PM
Code only requires the switch. As to where when you have multiple doors/access, it doesn't care.
If you have an inside and outside access way to the basement or crawlspace, the code does not care which door/access way the switch is at. Most code inspectors(in this area) prefer it at the inside access way. But can't fail you for it being at the outside access way.
stickboy1375 06-27-2012 05:45 PM
12 Attachment(s)
How about an actual code section? Im just curious what section this falls under.
beenthere 06-27-2012 05:54 PM
Not at my normal desk. will look section up later.
stickboy1375 06-27-2012 05:54 PM
12 Attachment(s)
Great, thanks...
beenthere 06-27-2012 08:29 PM
NFPA 31:
10.5.1*
Oil burners, other than oil stoves with integral tanks, shall be provided with some means for manually stopping the flow of oil to the burner. Such device or devices shall be placed in a readily accessible location at a safe distance from the burner.
10.5.1.1 For electrically powered appliances, the requirement of 10.5.1 shall be accomplished by an identified switch in the burner supply circuit, placed near the entrance to the room where the appliance is located.
stickboy1375 06-27-2012 08:33 PM
12 Attachment(s)
Any clue to where electric fire o matics come into play?
beenthere 06-27-2012 08:44 PM
Mounted over the boiler near or on the ceiling, the handle melts at 160 or so, and shuts off the electric.
stickboy1375 06-27-2012 08:50 PM
12 Attachment(s)
I was curious of a code section on actual requirement.
biggles 06-27-2012 09:00 PM
the emergency switch is only that....the furnace should have a unit mounted service switch.i would relocate it up into the house hall closet near the kitchen high up on the wall..with its red plate
beenthere 06-28-2012 03:45 AM
Not in my IMC, or NFGC books. May be in the newest codes. But its not required in my area.