Nuisance Breaker Tripping - HVAC - DIY Chatroom Home Improvement Forum
Old 02-03-2010, 06:22 PM   #1
Rewards Points: 29
Nuisance breaker tripping
On 2 occasions this winter, the 30 AMP breaker for my near new (aug. 09) heat pump has tripped. The unit is a Goodman 4 ton SSZ dual fuel (propane).
Today when it tripped the outside temps were in the mid to upper 30's. I have a clamp on amp meter so I put it on each leg while the unit was running, 15.x amps each on both legs. Shut the unit off, turned it back on and waited for the wait cycle to finish and watched the amps on start up, it happens very fast but it appeared to hit 69 or so for a split second (this is normal, I think for motors), then fell back to 13.x then as the unit ran, slowly climbed to 22.7 where it seemed to top out, then after a while it would go down slowly to 15 or, then back to 18.
I put new 8 gauge copper wire in from the panel to the box outside while the HVAC guys were working on installing the heat pump, so there is room to go to a bit larger breaker maybe but that probably isnt' the thing to do.
Not sure what to think....the unit works great and the only other thing thats a bit out of the ordinary is that it does "moose call" on occasion when the reversing valve switches). Probably does that once every couple weeks. The weather here for the last several months has condusive for ice making, very high humidity.
Hoping that beenthere and you other guys in the know can maybe point me in the right direction, it's so sporadic that I'm not sure calling the hvac guys back would be helpful.
Dave Carney is offline   Reply With Quote
Old 02-03-2010, 07:09 PM   #2
Rewards Points: 502
The "moose" call is it going into defrost mode, perfectly normal.
What is the manufacture recommendation for the breaker for the outdoor unit?
What is the model number of it?
-Andrew
DIY hobbiest
AndrewF is offline   Reply With Quote
Old 02-03-2010, 07:25 PM   #3
Check the breaker size on the name plate. Also check the capacitor.
Old 02-03-2010, 07:32 PM   #4
Rewards Points: 29
From the install manual...
Minimum circuity ampacity 25.9
Maximum overcurrent protection device 40 amp
Model SSZ160481
RLA 19.8
LRA 109.0
Condensor fan motor 1/6 hp
Old 02-03-2010, 07:55 PM   #5
min ampacity is for wire size. Over currant protection is the fuse, can be a 40 amp.
Old 02-03-2010, 11:14 PM   #6
An old Tradesmen
Rewards Points: 6,846
You have 8 guage wire. I would install a 40 amp breaker.
When the unit goes into and comes out of a defrost cycle. The amp draw can jump fairly high until the unit stabilizes again(for the length of your moose call and about a minute or 2 after that).
Your system charge is probably not as close to correct as it should be(cause of the moose call, not the breaker tripping). I think the reversing vale in that unit is big enough for a 9 ton unit. So if the charge is a little low. It doesn't switch as well as it should.
Old 02-04-2010, 07:59 AM   #7
Rewards Points: 29
Thanks man. Before I read your post I ordered a new 35 amp breaker. Maybe should have went 40 I guess but if it still trips the 35, I'll wait until it warms up in late spring and have them check the pressures. The reason I went 35 was that there is a 3 foot run of 10 gauge wire from the generac (whole house generator) transfer panel to the 8 gauge that I ran. (They come together in the original electrical panel) I'm well within limits still at 35 i believe, since that is a very short lead.
My other option I guess is to eliminate the lead altogether and move the 8 guage to the transfer panel direct to the breaker but it's not really set up very well for that and I'm trying not to make it too confusing for whoever owns it after me some day.
Old 02-04-2010, 12:41 PM   #8
An old Tradesmen
What kind of connection is there from the 10 to the 8 guage.
Old 02-04-2010, 12:59 PM   #9
Rewards Points: 29
It's the large twist on plastic connector used by the electrician that originally put in the generator. I re-used it, it's not a crimp on or anything. Is there something better to use?
Old 02-04-2010, 01:21 PM   #10
An old Tradesmen
Post pic of connection.
Old 02-04-2010, 08:42 PM   #11
Rewards Points: 29
Sorry for the delay...was busy getting laid off at work... :=(
The big blue wire nuts are the connections...
Old 02-04-2010, 08:55 PM   #12
An old Tradesmen
Not the best for the start load the compressor will have.
Old 02-06-2010, 01:59 PM   #13
Rewards Points: 29
This morning I rerouted the 8 gauge direct to the breaker in the generac transfer panel. Left it on the 30 amp breaker (for now pending results)
Pool Main breaker keeps tripping beckyreyes Electrical 12 08-11-2013 04:06 PM
Dead Breaker? and Nusiance Tripping... jasonblu Electrical 9 11-06-2009 06:13 PM
New GFCI Breaker Tripping w/ 3-way Flourescents BigJimmy Electrical 8 12-29-2008 02:29 PM
Tripping Wrong Breaker woodworksnmore@comcast.ne Electrical 15 03-28-2008 01:47 PM
20 Amp Breaker tripping with GFCI panhandlion Electrical 7 12-12-2007 08:59 PM