#1 |
noisy blower / filter box redo
Right now my furnace sounds like a train engine... when ever it speeds up to high speed that is (claims at .5" WC it should be doing 2028 CFM, if I change the jumpers to run at low speed which at .5" WC it should be doing 1287 CFM the noise goes away... which leads me to believe that either the return is undersized, or the blower is just loud as heck.... now other furnaces I've seen when running full speed you barely notice them, this one you can hear running through walls...
the total conditioned Square footage of the house is ~3,800 sq.ft. Basement: 1500 1st Floor: 1500 2nd Floor: 830 the furnace install documents say this about the return: Return opening 19 x 21 5/8 minimum filter size 15 1/2 x 25 right now the return has a 16x24x1 filter... the return duct coming from the boot is 24x8, which turns into 2 separate 12x8 ducts (that is what about 1,200 CFM? not sure since I dont know the velocity and true WC of the design) Furnace Info: * has a 4 ton condenser unit on it (R-22 refrigerant) * 125,000 BTU/h * 92.1% AFUE * 3/4 HP blower motor * 12 x 12 blower wheel size what I would love to do is get a media filter on here, but not sure what size would fit the furnace.. Was looking at the Honeywell F200E1037 CFM: 2,000 WC drop: 0.28" Opening Dimensions: 23.25W x 18.44H inches Dimensions: 25.5W x 20.18H x 6.75D inches wasn't sure if that was too big, the wrong size, etc... it's the closest I could find size wise to the return opening on the furnace, and the filter size is 20x24x4 which is a little more interns of sq inch for the opening area. I know you don't want the return velocity too high or stuff will be sucked right past the filter or not filtered properly, and it seems like its trying to pull more then it can get through right now which might be the cause of the noise... if you ever had a oh say 4' x 4' sheet of sheet metal and moved it around to make a thunder like noise, its close to that sound when running just a little bit quieter. So I am thinking this return needs to be taken up to the following: * Larger filter area, hoping media filters will help since they have a ton more surface area then a flat filter * Larger return boot and stack, right now the stack off the boot is 24x8, should be at least 24x10? * increase the size of the return trunks, right now they are 12x8, maybe 16x8 each way? |
#2 |
If the blower motor is making noise the bearing is going bad.
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead. |
#3 |
it's not the motor though as far as I can tell, the noise sounds like never ending thunder like if you pushed in on a plenum then let it push itself back out
if you take the blower out and run it by itself its pretty quiet minus the air disruption caused by it I looked up the original fact sheet that aire-flo (lennox) gave out on this furnace and it says it should be "extremely quiet", definitely not what I am experiencing |
#4 |
Remove the return grid and check if the noise will get strong.
#5 |
that's what I am hoping on doing tonight to test.... that and trying the other speeds the blower runs at to see if its any different...
AC wants it to be on High though to work efficiently apparently, and thats where all the noise is at when its trying to draw 1600 to 2000 CFM (not sure which one it is for this model with the current duct design) |
#6 |
In cooling mode the the blower motor should be set in high speed. Check if this blower motor is the correct.
#7 | |
noisy blower / filter box redoQuote:
the blower motor is the original part number, so I think its the right one. the furnace is only 4yrs old |
#8 |
To be able to check static pressure you'll need a Manometer. But you can focus on the noise issue since cooling speed is set to high speed.
#9 |
Hvac Pro
4 ton AC x 400 cfm/ton = 1600 cfm max. No more required. Carrier is now using 350 cfm/ton on the newer units so that = 1400 cfm. With a TX valve and ECM motor you can safely run it at 1400 cfm . De-humidifies a lot better at the lower cfm but you should get the subcooling checked to be safe.
"Cut it twice and it is still too short". To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. Last edited by yuri; 07-14-2011 at 06:32 PM. |
#10 |
8x24 isn't anywhere near big enough blue. 1600cfm and you want 400fpm max at the drop so the duct needs to be equal to 4 square feet. Usually the big 4 and 5 ton units are better off with half coming in from each side. I bet you have more then a half inch of static just on the return side.
#11 | |
4 sq ft... humm, this will be interesting to figure out... might just have to call a pro in to do some calcs.... I knew it was undersized with the 24x8 return, my parents house is half the size of mine and their return is 24x16! and their furnace is extreamly quiet running at high speed |
#12 |
CFM/2 = sq.inches of area.
2 ton 800/2 = 400 sq.inches 3 ton 1200/2 = 600 sq. inches 4 ton 1600/2 = 800 sq. inches 5 ton 2000/2 = 1000 sq. inches
#13 |
30 year tech
Furnace seems way oversized for the house. Where do you live?
Most furnace manufactures want you to come in on both sides for 2000+ cfm. As said you don't need that much air for the air conditioner. Sounds like your whole return air duct system needs to be redone. What's the make and model of the furnace? |
#14 | |
Aire-Flo Model: AF92MPE125U5B I think its a 1,600 CFM furnace |
| Display Modes | |
| Bryant Plus 90 - No Blower | Ducaticorse | HVAC | 11 | 10-16-2012 09:39 PM |
| Inground pool and filter...HELP! | Blpavlovich | Building & Construction | 2 | 06-09-2011 06:49 PM |
| Noisy Fan Blower during start up | shabtay | HVAC | 9 | 03-23-2011 06:15 PM |
| Forced Air Blower is too noisy, blows too much air too fast | hawks81 | HVAC | 6 | 07-06-2010 08:09 AM |
| Carrier 58MXA Wiring Blower Switch | 63012753 | HVAC | 0 | 10-06-2009 10:09 PM |