Old 11-11-2008, 03:34 PM   #1
No voltage no blower comfortmaker furnace
Hi, Have a Comformaker 80 furnace with electric ignition that quit working. No response from jumping red an white wires on thermostat. Checked transformer and have 24 volts there. Blower does not come on, no ignitor either. I have power to furnace, on off switch is good, I can hear slight hum of transformer when blower door switch is held in. Any ideas short of calling a service man? Thanks
milender is offline   Reply With Quote
Old 11-11-2008, 03:40 PM   #2
limit switch is what im thinking although it usually makes the fan run when they trip secondly i would be thinking the boards bad probably about 50 to 75 dollars if all limits are closed and you have 24v between white and common at the board prolly the board
kennzz05 is offline   Reply With Quote
Old 11-11-2008, 07:35 PM   #3
Hi, yes it was a broken wire at the limit switch, reconnected and now have heat. Thank You.