I woke up this morning to a cold house. My furnance was running but there was no heat. The burner and pilot were out. Please help?? We have been in this house for 4 years now and have always had problems with it. We have changed the coupler, the ignitor and the thermostat.
concal is offline   Reply With Quote
Old 02-22-2011, 12:12 PM   #2
No heat gas furnace
Basic sequence of operation:
1. Thermostat calls for heat
2. Inducer draft motor is energized ( small blower connected to the flue inside the furnace.
3. The pressure switch makes enabling the ignitor.
4. the gas valve will now energize sending gas to the burners.
5. Main blower comes on and stays on untill the thermostat shuts it down.
Watch your unit start and check this sequence and see what doesn't happen and let us know.
college A/C is offline   Reply With Quote
The Following User Says Thank You to college A/C For This Useful Post:
concal (02-22-2011)
Old 02-22-2011, 12:51 PM   #3
No heat gas furnace
The blower continuously runs and the thermostat calls for heat but it won't ignite
Old 02-22-2011, 02:30 PM   #4
hvaclover's Avatar
No heat gas furnace
You could have an open limit which turns off the gas when the furnace over heats.
How old is the furnace and a model number would help greatly.
And what would be the best is if you can post pics of the furnace with the top and bottom removed.
Just slow, not stupid.
hvaclover is offline   Reply With Quote
Lennox Furnace G27M Series – Unreliable operation: pressure switch or else? sheppard1977 HVAC 7 01-14-2013 06:42 PM
How to stop auxillary heat from coming on defrost cycle and limit auxillary heat use? twilightcall HVAC 34 12-28-2010 07:53 PM
Using Gas heat during Defrost mgroves HVAC 15 12-18-2010 06:51 PM
uneven heat: testing ceiling radiant heat /finding cables/fix cables martinradiant Electrical 1 10-03-2010 09:22 PM
Heat Pump Blower always on gg_daman HVAC 1 12-16-2009 07:15 AM