No HEAT! Ch-240 navien how to Purge ?? Where is the fill valve?
Need to know how re add water (purge?) Into my navien heating system.
I thought rhe water feed would do it just by turning valve back on but apprently
There is a different way to add water.
The system was drained to add additional baseboards now cant figure out how to get water back into system
Need to locate the Fill valve on here. Anybody know which night this be in pic?
Mikee_s_1975 is offline   Reply With Quote
Old 01-04-2013, 04:59 PM   #2
Pic
Heres pics ! Might it be the valve in the darker close up image, this valve is marked " aut9 feeder water inlet" and is off
No HEAT! Ch-240 navien how to Purge ??-1357340281640.jpg   No HEAT! Ch-240 navien how to Purge ??-1357340410609.jpg   No HEAT! Ch-240 navien how to Purge ??-1357341925096.jpg
Old 01-04-2013, 05:51 PM   #3
An old Tradesmen
Rewards Points: 6,836
So there isn't any water pipe connected to the auto water feeder connection on the boiler? Manual designates it as H. I see a back flow preventer piped to it. or at least it looks like its piped to h.
Old 01-04-2013, 06:01 PM   #4
Yes there is a water feed going into "auto feeder water inlet" on bottom.of the boiler. There is a valve on this, this this valve is it. Should I just turn it on for a few to fill up system?
Old 01-04-2013, 06:09 PM   #5
An old Tradesmen
Turn it on. but have a hose connected to that valve that i said in the other thread and purge your system of air.
Old 01-04-2013, 06:27 PM   #6
Seems to keep going, the hose has been running for 10 min now, is this normal?
Old 01-04-2013, 10:33 PM   #7
An old Tradesmen
Did you have the valve below where the hose was connected closed. if so, 10 to 20 minutes is not unusual.
Old 01-05-2013, 12:13 PM   #8
The Token Engineer
Boiler piping is wrong, check manual
Im surprised you would ever have much heat at all, its piped wrong.
Looks like an attempt at a primary loop off the boiler but the drops between the boiler and the loop are tied together which is wrong.
The boiler flow will never pass by the secondary tees, only heat you get is a bit of gravity/conductive flow. Example on right is best way to get most efficiency and heat transfer requiring you to do some small piping changes.
Also the auto feeder can not feed fast enough to purge your loops above the boiler, proper valving and manual purging is required.
zl700 is offline   Reply With Quote
Old 01-05-2013, 12:20 PM   #9
The Token Engineer
Easy to do
Easy fix to do before filling, the changes will make it perform 500% better
BTW, the autofeeder on the Navien CH water valve should always be left on, it feeds the correct water pressure electronically.
Old 01-05-2013, 12:21 PM   #10
The Token Engineer
maybe this pic will show up
VisionPRO Setup Functions & Heat Pump infoskr HVAC 43 07-12-2015 04:28 PM
Heat won't stop running, just installed new thermostat NorthSidePK HVAC 28 11-01-2012 10:05 AM
dual fuel heat pump - no heat without propane sweetfarm HVAC 3 10-11-2012 08:07 AM
Comparison and Heat Pump Selection help... ChrisDIY HVAC 7 03-06-2010 08:34 PM
Heat Pump Woes Zenica HVAC 50 01-27-2009 07:37 AM