No Delay Of Blower ON For Rheem Electric Furnace? - HVAC - DIY Chatroom Home Improvement Forum
Old 11-09-2013, 02:12 PM   #1
Rewards Points: 1,554
No delay of Blower ON for Rheem electric furnace?
Rheem Electric Furnace/Model# RBHA-17j15sfa (an older unit)
Is it normal for this blower to not have any ON (start-up) delay when the t-stat turns the unit on? (compared to a standing pilot gas furnace that heats the heat-exchanger up first, then turns blower on?)
justplumducky is offline   Reply With Quote
Old 11-09-2013, 04:04 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 1,452
lesson 4 U. if you get an electronic tstst and set the switch to elec instead of gas it will energize the G terminal and start the fan instantly which is the way it is supposed 2B. some elec furnaces use contactors instead of sequencers and W pulls in contactors and a fan relay with no time delay.
The Following User Says Thank You to yuri For This Useful Post:
ben's plumbing (11-09-2013)
Old 11-09-2013, 04:40 PM   #3
Thank you for the lesson. Is it because the heating element(s) would get too hot unless air is already moving when they're switched on?
Old 11-09-2013, 06:54 PM   #4
Hvac Pro
yuri's Avatar
no. it is just the way they do it w/o sequencers.
Old 11-09-2013, 07:47 PM   #5
On this particular unit, 24vac Red wire leaves transformer mounted on furnace cabinet, goes to t-stat, comes back on White wire from t-stat, connects to three individual wires at furnace cabinet, two of which feed the two heat sequencers (brass quick disconnects at base of sequencers) - the third one feeds the hot side of Fan Relay coil.
The opposite side of the heat sequencers (brass q-d's at base) and the common side of Fan Relay coil all connect to common of transformer mounted on cabinet.
As I've described the wiring connections above, the Fan/Blower will energize immediately with a call for heat, but there will be a slight delay (per the timing of the heat sequencer) of the first heating element(s) turning on. Correct? This would give an initial blast of room temperature air, before the sequencer energizes the first heating element(s). Is that normal/acceptable?
Old 11-09-2013, 07:54 PM   #6
Hvac Pro
yuri's Avatar
Yes, sequencers REALLY are there for where I am and you have 30 kw furnaces with 6 elements. the power co does not want 6 of them hammering on at the same time as lights will dim etc. electric furnaces are not really designed to be very deluxe or have comfort features just do a basic job.
Old 11-09-2013, 08:03 PM   #7
The depth of your answers is much appreciated. Have a good night.
Old 11-09-2013, 08:45 PM   #8
When the call for heat is removed, I believe these heat sequencers de-energize the heating elements in delayed, reverse order, but the Fan/Blower will shut down instantly when call for heat is removed. This unit is a 15 KW unit/ a total of 3 individual, crescent moon-shaped "Calrode" (so I've seen them called online) heating elements. Would that be a problem for this unit?
Old 11-09-2013, 11:21 PM   #9
Hvac Pro
yuri's Avatar
Ideally it is better to have the fan shut off after all the elements but the manufacturer did not seem to care IMO plus those old school elements were tough as nails and did not seem too care either. Nowadays they hook them up to sequencers or a time delay relay on these condo units etc.
justplumducky (11-10-2013)
Replace furnace or blower agibby5 HVAC 6 07-17-2012 07:17 PM
Gas furnace blower AC retrofit problem agibby5 HVAC 0 07-09-2012 07:58 PM
Carrier Furnace code 33 @ startup blower fan sounds like jet Frank Ottawa HVAC 6 04-19-2011 08:12 AM
Bryant Gas Furnace - blower sarts and stops montepix HVAC 7 12-24-2009 05:11 PM
electric furnace need help Unregistered HVAC 3 10-16-2007 03:41 AM