No 24V to gas valve - Cold - Please help
Greetings,
I have an older Carrier 58ss that water from the collector leaked and
made its way to the blower control circuit board. We started having a
problem with the fan always being on so we called the company we have
service the furnace and AC come out. When the guy turned the furnace
on the blower control board shorted and started a fire(quickly
extinguished). I know I need to replace the furnace, but I have a cash floe problem right now.
The control board part was HH84AA005 is obsolete, the Carrier
replacement is HH84AA021. I also replaced the tranformer(scorched by
the flames) and the relay on the inducer board(corroded contacts from
the water dripping down). After installation, everything worked except
that there was no 24V to the Pick coil (terminal #3) of the gas valve.
While it is supposed to be a drop in replacement(if you believe the
docs), the board is significantly different with additional functions
and features. One big difference is that 10B1-2 that needs 24V can be
traced directly to the C terminal which goes straight to ground through
a plated mounting hole on the circuit board. There is no grounding on
the old board at all.
I have heard there is a service bullitin with modifications
required to make HH84AA021 work in a furnace that was shipped with a
HH84AA005? Does anyone know where I can get the information? Any other insights would be greatly appreciated.
Thank you very much,
Bob