I installed a 20 kw Goodman in for a business for there kitchen less than 800 sf it was working fine had 90-92* coming out now a week later the heat is 76-81* coming out temp in kitchen wont raise past 63* any body have a suggestion I am pulling 48 amps both stages is on fan is set on low speed
jkv is offline   Reply With Quote
Old 12-26-2012, 02:43 PM   #2
Hvac Pro
sounds like 2 elements are not working. each element should draw approx 20 amps. W=ExI watts = volts x amps 5000/240 = 20 approx.
Old 12-26-2012, 02:56 PM   #3
jkv
Thanks, I can check them and see the bad thing is goodman wont warranty the heat strip
Old 12-26-2012, 03:35 PM   #4
Hvac Pro
may be a sequencer not turning them on.
Old 12-26-2012, 03:50 PM   #5
jkv
Thanks, I will check both of them
Old 12-26-2012, 04:20 PM   #6
Hvac Pro
check if there is a "low" heat switch on the cover. some brands have one to disconnect 1 element for Fall use so you run 3 elements in mild weather and 4 in cold. could also say mild or other description. staff may have fooled with it.
The Following User Says Thank You to yuri For This Useful Post:
LanceV (12-26-2012)
Old 12-26-2012, 04:46 PM   #7
An old Tradesmen
Depending on the air handler. low fan speed is too slow for 20 KW, and can cause a thermal to stick open.
Old 12-26-2012, 07:36 PM   #8
jkv
That makes since You may be right I checked everything tonight and all is fine but the second stage is not coming on so I will look at that thanks
Gas Furnace Hiccups hugocraft HVAC 2 12-22-2012 07:50 AM
Need Help With Furnace Install 67Dart440GT HVAC 6 10-20-2011 09:40 PM
Install Help on 75K BTU Garage NG Furnace live4spd HVAC 23 10-15-2011 08:58 AM
New Cased Coil - Install to Furnace - PICTURES!! hartkem HVAC 39 11-18-2008 02:45 AM
Installing a new Furnace, Shoud I install an A/C Coil Now? hartkem HVAC 1 11-10-2008 10:31 AM