i want to update my ductwork in my house, i think it should be very easy as i live in a 1 story ranch and i tore my whole basement out and is accessible and the current trunks are straight runs. it would take me 10 minutes to tear out the old stuff. they are original and dirty as hell and i think too small for my house. where can i find or how to figure out what size i should get so i can get even flow through my house? i also want to move one register over 2 bays so it isnt being blocked by couch. im sure it isnt as easy as it seems but it doesnt look too difficult at all once i get my calculations. are there certain sizes for code now too? thanks
beenthere 03-22-2013 08:28 PM
Need to know how much air each room should have. And then can size trunk line based on that.
jhack836 03-22-2013 09:08 PM
i have 4 bedroonms aprox 11x11
2 bathrooms aprox 7*5
living room approx 20*15
dining room/kitchen aprox 15*8
basement approx 80*25
or should i get exact sq ft numbers instead of a approx?
the trunk i have downstairs is 9.5 wide by 8 in tall and 15ft one way off the furnance and the other trunk is 8ft in opposite direction right now. furnace is in the middle of the house
i got a new high eff furnace last yr but forgot what the btu was but i know it was enough to work if i ever finished the basement too
beenthere 03-22-2013 09:19 PM
Actual sizes.
What you posted makes your basement bigger then your first floor by 1,026 sq ft.
First floor came out to 974 sq ft, basement came out to 2,000 sq ft.
jhack836 03-22-2013 09:58 PM
Originally Posted by beenthere (Post 1143487)
Actual sizes.
ok i will measure in the morning, i will double check them tomarrow. i over estimated basement. i was thinking linear feet becaus of my gutters but included my garage.
jhack836 03-23-2013 11:11 AM
ok i was pretty close on some of my estimates..
BR1 13*12
BR2 11*11
BR3 12*10
BR4 12*11
BATH1 7*5
BATH2 6*4
HALLWAY 17*3
KITCHEN 12*7
DINING ROOM 10*10
LIVING ROOM 19*14
BASEMENT 48*25
so if i calculated right the main floor and basement should beabout the same right around 1100-1200 sq ft each
jhack836 03-23-2013 11:23 AM
with the furnace almost center in my basement the current trunks i have are 24ft long and are 8in wide by 9.5in thick and the other trunk is 11ft by 8in by 9.5in
the cold air return trunk is 7ft long by 15in wide by 8in tall
the return off the furance that connects to the trunk is 22in wide by 7in by 6.5ft tall
i installed a new 95% eff coleman furnace a yr and half ago but i have to find my book to get the specs on it.
registers..
1 in each bedroom
1 in each bathroom
2 in living room
1 in kitchen/dining
so 9 total registers in my house
jhack836 03-23-2013 01:00 PM
its a coleman 95.5% afue single stage multi position furnace, is there anything else you need to know to get the calculations i need? do you need the a/c info? thanks
beenthere 03-23-2013 02:27 PM
Size of furnace and A/C.
jhack836 03-23-2013 03:20 PM
furnace
btu input 80000 output 76000
1200 nominal cfm
33in high 29.5in deep 17.5 width
is that what i need to let know know for the furnace? i appreciate the help!
beenthere 03-23-2013 03:37 PM
Br1 125CFM 7"
br2 97CFM 7"
br3 96CFM 7"
br4 106CFM 7"
bath1 28CFM 4"
bath2 19CFM 4"
hallway 41CFM
kitchen 67CFM 6"
dining 80CFM 6"
living 214CFM 1-7" and 1-6"
Can't give trunk sizes since i don't know which branches are off which trunk line.
Basement should have it own trunk line. Above sizing allows 323 CFM for heating the basement.
jhack836 03-23-2013 03:46 PM
the 11 ft trunk has registers for..
BR1
BR2
BR4
BATH1
BATH 2
the 25 ft trunk has
2 IN LR
KITCHEN
BR3
the basement doesnt have any registers, it just has 1 vent in the 11ft trunk and 3 vents in the 25ft trunk. some day i would like to finish half the basment(the side with the 25ft trunk) which would be about 27*25 so 675sq ft.
beenthere 03-23-2013 04:00 PM
Your furnace is most likely over sized, and probably blows out hard at the registers nearest the furnace. So run a trunk line for the basement now while your doing the other 2.
The 11 foot ;ong trunk can be 10X8. The 25 foot trunk can be 14X8. A trunk line for the basement can then be 10X8.
jhack836 03-23-2013 04:11 PM
Originally Posted by beenthere (Post 1143963)
Br1 125CFM 7"
br2 97CFM 7"
br3 96CFM 7"
br4 106CFM 7"
bath1 28CFM 4"
bath2 19CFM 4"
hallway 41CFM
kitchen 67CFM 6"
dining 80CFM 6"
all the lines i have now the run off the trunks to the registers are 7in
beenthere 03-24-2013 03:07 AM
They can all stay 7" then.