New Control Board Or Fix It? - HVAC - DIY Chatroom Home Improvement Forum
Old 01-17-2012, 05:33 PM   #1
Question
New control board or fix it?
I'm assuming I need a new control board for this furnace. Maybe it can simply be repaired or isn't even the problem in the first place.
Carrier Weathermaker 9200 58MXA
Part # on current control board is HK42FZ016
I'm thinking of getting the ICM282 as a replacement. Working on small electronics doesn't bother me so if this cheaper board does the job once it is installed I'm not paying OEM prices just so it looks the same.
Here's my problem though. (this furnace has been running fine for 10 years) The induction fan comes on, the fire starts, no error codes are flashed but the instant the blower comes on the flame goes out. The blower runs for a minute while it flashes the code 12 (one short two long) and then shuts off. Code 12 just says the blower is running for 90 seconds after a call for heat (R-W closed). What is "R-W closed" anyway, maybe this is my problem? Ten minutes later it cycles through this again and it never ends. Flame sensor looks basically new. I cleaned it a touch with some 1200 grit sand paper but that was purely cosmetic I think. If I leave it disconnected I get error codes so I'm assuming it works.
The trouble shooting guide leads me to checking the DC microamps on the flame sensor wire. This guide is confused though because it first says "Is the DC microamps below 0.5?" and then in the very next troubleshooting bubble is says the "current is nominally 4.0 to 6.0 microamps". So which is it, 0.5 or 5.0? Doesn't really matter though because my amp meter is a Fluke t5-600 and won't measure these small amps anyway. So as I mentioned I'm assuming the flame control sensor is working and it's a problem in the control board.
Can I fiddle with some jumper settings on this board and get it to work? Clean it maybe? I don't know, I'm grasping at anything that isn't a $200 plus OEM board.
Thanks in advance for any useful information about this. I hope I've explained it well enough.
Bobeht is offline   Reply With Quote
Old 01-17-2012, 05:56 PM   #2
I'm Your Huckleberry
Rewards Points: 2,270
How does the system perform in "fan on" or "cool" ?
Thanks.
Doc Holliday is offline   Reply With Quote
Old 01-17-2012, 05:57 PM   #3
biggles's Avatar
"R to W closure" indication is the heat call from the stat then the rest is the board as should the Induced Draft motor is the first to run from that R/W call...if it is only getting a pilot but no burner when fan starts sound like the board..but i'm not spending your money on that let other kick in model and brand and honeywell stamped number on the board so they have something to work with.... check them here http://www.bestbuyheatingandaircondi...cuitboards.htm
Old 01-17-2012, 05:57 PM   #4
your manual is correct. .05 micro amps is the minimum flame signal reading the burners will stay lit at. The normal range a clean sensor will read is between 4 and 6 micro amps. You need a DC micro amp meter to read it.
hvac5646 is offline   Reply With Quote
Old 01-17-2012, 06:02 PM   #5
R-W closed mean while on call for heat the entire furnce (control board) is losing power, power is interupted. When power is restored to the board the blower comes on again with the 90 second "on" time delay.
Your board is most likely malfunctioning at this point or judging by your description of what is going on I'd have to assume so. A board should never lose power and come back on with a time delay unless actual high voltage power has been turned off to the unit and turned back on again.
It should never do it during a call for heat or otherwise.
You can pull the board off and look on the back for any burn marks.
Thanks.
Old 01-17-2012, 06:04 PM   #6
This.
..and since one smiley is not enough to reply to a thread, this too..
Thanks.
Old 01-17-2012, 06:08 PM   #7
OP, are you saying that while on call for heat the initial heat sequence begins all the way through to when the blower comes on (last) but as soon as it does the unit goes to fault code 12/90 second blower on, turning off the heat in the process?
If that is the case then you need another board. I wouldn't even mess with the old one.
Thanks.
The Following User Says Thank You to Doc Holliday For This Useful Post:
Bobeht (01-17-2012)
Old 01-17-2012, 06:18 PM   #8
Good idea Doc, I'll go pull the thing and see if it's burnt. It has no funky smell like so many other fryed electronic devices I've been responsible for destroying but it's also hard to see well where it is now. To biggles post, it's not just a pilot burning, it's the full on flame in each heat exchanger burning away like it's supposed to. It blows luke warm air for the 90 seconds the blower is on because of the burner being on for a minute or so before it goes out.
Old 01-17-2012, 06:39 PM   #9
Yes, exactly this. You've answered what I needed to know I guess. Thanks for that. Any advice on if I can do better (cheaper) than the ICM282? I saw an ICM282A but I doubt I'd need the options it has over the original.
Old 01-17-2012, 06:47 PM   #10
biggles's Avatar
leave the board off the mounting(slip a piec of cardboard to support it),and then restart it with everything connected...might need a ground jumper that a screw would provide just in case it just sits there see if you get a different sequence..even fan vibration might be effecting the board signal for the main burner....just thinking out loud...didn't see your unit info first time reading... DAH sorry
Old 01-17-2012, 08:15 PM   #11
A new development has arisen. I liked biggles' idea about messing with the board. So I did. It was a little more of a pain then I wanted so instead of removing the board mounting entirely I popped it loose but basically left it there. It wasn't loose everywhere but most places. This time when the blower came on the burner lasted a couple of seconds before it quit. Any change is good I'm thinking so I blew everything out with an air hose and hooked it back up. The thermostat is upstairs of the furnace so I wanted to shorten my trips. First thing I did was blow the 3 amp fuse by shorting the thermostat wires to the ground with my screw driver, entirely my bad for being sloppy but I found a 5 amp and put it in there for today. I unhooked the thermostat wires (only had 2) and hooked up a 3 foot chunk of speaker wire to hang out of the furnace instead. When I twist the wires together the furnace operates just like it should. Of course it'll stay on forever if I leave it like this but now I know the control board is apparently fine and the thermostat is the problem. This is old school tech here, just a temp sensitive spring and a contact point. I don't see how a thermostat that could be from the 70's is the problem but it is. It is just a contact point after all.
Doc first asked me about a "fan on" or "cool" option. I'm guessing I somehow have the option to have this thing hooked up to just circulate air. Maybe if I get the right thermostat I can do this I'm thinking? That would be nice for summer but it's never been an option the way it was installed.
Old 01-17-2012, 08:49 PM   #12
Old 01-17-2012, 09:07 PM   #13
Nice! I would not have thought the stat would be the problem.
If your board in the furnace has terminals R,Y,G,and W and of course it does then you certainly can get a stat with the same terminals, all new ones do, and hook it up.
R is your constant power to the stat, Y would be cool, W would be heat and G is fan only on. Just connect from stat to furnace exactly to the same terminal on each, stat and control board.
Turn off the power to the furnace first, don't want to blow another fuse.
Thanks.
Old 01-17-2012, 09:25 PM   #14
how
Rewards Points: 1,104
My vote goes to the 3 amp fuse being changed for a 5 amp or some change on the board with the removal and remounting because the thermostat circuit bypass just doesn't make any sense.
how is offline   Reply With Quote
Old 01-17-2012, 09:30 PM   #15
The plot thickens...
Thanks.
Bad control board? juddskee HVAC 12 12-24-2011 09:59 AM