New 22' Trunk Line - HVAC - Page 2 - DIY Chatroom Home Improvement Forum
Old 05-21-2010, 01:15 PM   #16
I finally got the information entered into HVAC calc. It's showing gain of 22376BTU and a loss of 54843
THe RGFD-06EMCK that I'm thinking of getting is 55800BTU. That 1.7%
I think I'll need to triple check hvac calc and make sure my load is correct.
unixb0y is offline   Reply With Quote
Old 05-21-2010, 01:31 PM   #17
Looks like I was missing the basement walls.
Old 05-21-2010, 01:43 PM   #18
An old Tradesmen
Rewards Points: 6,086
So what size is your current A/C?
I don't see anything added for your kitchen appliances.
What infiltration rate did you use?
Old 05-21-2010, 02:12 PM   #19
It's a Carrier 38RE030 installed in 1982.
I guess I'll have to read more about this in the hvac calc manual.
I used poor. The house was built in 1945. But I have triple pane windows from 1988.
For the walls I used R11. It has the original siding on. I know that there were the following retrofits
1) Cellulose was blown in at one time
2) Aluminum siding was added and there is some foam attached to the sheathing.
Changing the infiltration to average seem to drop the cooling to 1.5ton and the heating to 44000 BTU.
I did have an infiltration test done before BUT that was with a 6" make up air, 6" fresh air and 7" chimney.
Those results were:
5.03 ACH(Air Changes per hour) @ 50Pa
Equivalent air leakage: 860cm2 (334.6 inches squared).
Old 05-24-2010, 12:00 AM   #20
Originally Posted by unixb0y View Post
Those results were:
From the googling I did, It looks like the ACH can be divided by 20 to get the infiltration rate. That gives me an infiltration rate of 0.2515.
That seems low considering the value that can be set in HVAC-Calc. I guess I'll use the setting of average in HVAC-Calc.
Old 05-24-2010, 12:48 AM   #21
I'd ask Beenthere about that first. I have heard there are some discrepancies in the soft ware.
hvaclover is offline   Reply With Quote
Old 05-24-2010, 05:07 AM   #22
An old Tradesmen
How dry was/is your home in the winter?
Do you have to use a humidifier to keep the house from getting to dry?
If no to any of the above questions. Using .25, or tight in HVAC calc is fine.
Old 05-24-2010, 11:17 AM   #23
We have been living in the 1945 house for 4 years now. The house had a humidifier BUT it's not connected. It got disconnected during a past galvanized pipe to copper conversion.
I'm not sure under what circumstances we would use a humidifier.
He haven't had a problem with static on carpet or clothing. I'm not sure if that helps.
Old 05-24-2010, 01:41 PM   #24
An old Tradesmen
A humidifier would be used in the winter.
If you don't have a low humidity problem in the winter.
You can use .25 for summer and .5 for winter infiltration.
Old 05-25-2010, 10:58 AM   #25
If I'm going to have a furnace, AC, Humidifier and possibly a HRV(in the future), What is the spec on the wiring to the thermostat?
Old 05-25-2010, 02:05 PM   #26
An old Tradesmen
Depends what thermostat you use.
Old 05-25-2010, 03:04 PM   #27
White Rogers 1F95-1291
Old 05-25-2010, 03:11 PM   #28
An old Tradesmen
That stat can't control a humidifier or ERV.
So for a single furnace, and a single stage A/C, 5 wires.
Old 05-31-2010, 07:01 PM   #29
I have noticed that some furnace installs have raised the furnace off the ground.
In one case, I presume this is an effort to reuse the plenum. THey used cinder blocks and dense foam insulation.
In another case, i suspect the installer wanted the keep the furnace off the concrete in case of the flood/damp basement. The installer used PVC pipe as legs to get off the floor.
Are there any other reasons to not put the furnace directly on the concrete basement slab?
Old 05-31-2010, 07:04 PM   #30
Do the cables come in 5 wire bundles?
Trunk Line Insulation Sype HVAC 4 01-18-2011 10:44 AM
Capacity loss with line size Einride HVAC 1 06-29-2009 04:10 PM
sewer line Master Brian Plumbing 3 05-25-2009 01:53 AM
how many take offs can you put on an 8x20 trunk line? jfranks76 HVAC 5 05-09-2009 07:17 PM
how many trunk line and feeder lines Grandma Lewis HVAC 4 03-08-2009 07:07 PM