Old 12-26-2012, 10:13 AM   #1
Need Help With Heat Strip Install
Hello all. I recently purchased my first home. It's located in northern oklahoma. It is equipped with a Goodman HVAC unit that was installed by the previous owner and a neighbor.
For the past few days the temps here have been between 9-20 degrees Fahrenheit. This thing would put out very little heat(if any) and run constantly. I pulled the side cover off, and realized the heat strip isn't even hooked up. The heat strip is also a Goodman MFG Mod# HKR-2CB
My main breaker box is rated 200amp and is located at the far East end of the house. There is a 100amp rated sub at the far West end of the house 55'-60' away. The wire between these is AWG 6 copper. Then there is approx 8' of AWG 6 from the sub to the unit. This is how it is currently wired up.
I would like to make this setup work as good as possible for the next few months as that is the soonest ill be able to replace the system. Going with propane.
My questions are;
Can I hook this heat strip to this sub?
Do I need a smaller heat strip?
Can I hook up half of the heat strip?
Are the wire sizes adequate?
Thank you for taking the time to read this and I hope it made sense.
davidwboyer is offline   Reply With Quote
Old 12-26-2012, 10:28 AM   #2
The heat kit in that unit is a lot bigger than what I would want to use and definately cannot be used with your setup but either way, having only 6AWG wire limits you on pretty much using anything with a heat kit.
If were me, I would leave what you already have for wiring and run another 6 AWG, line 50 amp breaker from the main box for a heat strip circuit but it wouldnt be enough to run what you have in there now, you would need to go with a smaller heat kit, something like an 8KW.
sammy37 is offline   Reply With Quote
Old 12-31-2012, 07:05 PM   #3
Thanks for the advice Sammy. I will get that done. Should work until I get the unit replaced. Then I'll use the circuit for an external outlet.
Old 01-01-2013, 06:41 AM   #4
An old Tradesmen
For temp use. I'd probably just run another 6 gauge to it and only wire in 10KW of that 20 KW package.
Old 01-01-2013, 08:40 AM   #5
use the 6 wire to run 10 kw of heat and run a new 10 wire for the unit to run on. i would not go with propane unless it is duel fuel
mrairflow is offline   Reply With Quote
Old 01-01-2013, 12:23 PM   #6
His main panel is 60 feet away, I would think number 10 would be a little on the light side for a 4 ton unit.
Old 01-01-2013, 02:36 PM   #7
Retired Electrician
looks like to me you have number 6 awg at the ac allready
fy171 is offline   Reply With Quote
Old 01-01-2013, 11:22 PM   #8
Yes, but that doesn't seem adequate to run the compressor AND heat strip at the same time. That's my dilemma. But I could be wrong.
Old 01-02-2013, 05:19 AM   #9
An old Tradesmen
Its only enough to run the heat pump and 5KW of aux heat at the same time.
No starter strip used on shed roof install? waterskier_erie Roofing 4 10-31-2011 09:25 PM
VisionPRO Setup Functions & Heat Pump infoskr HVAC 31 03-18-2010 02:15 PM
Reducing 15kw Heat Strip tx_reeg HVAC 22 01-24-2010 10:24 AM
Heat Pump Blower always on gg_daman HVAC 1 12-16-2009 07:15 AM
Heat Pump Woes Zenica HVAC 50 01-27-2009 08:37 AM