Old 01-12-2012, 07:11 PM   #1
mini split efficiency
I have a Mitsubishi four zone mini split system. The outside unit is 36K BTU. I installed just one inside unit at 15K BTU. I have been running this for 9 months now. It seems to run OK. I still have to install the remaining three inside units.
The Mitsu rep said that I should not run just one zone, but he doesn't know why. Does anybody know the answer to this? (I plan to install the remaining three zones ASAP)
Ron
rwfegley is offline   Reply With Quote
Old 01-12-2012, 07:20 PM   #2
May cause it to freeze up from not enough air flow.
Old 01-12-2012, 07:35 PM   #3
I speculated that it might be due to the fact that the unit is precharged for four zones, and with only one zone installed, the system is overcharged.
Old 01-12-2012, 08:13 PM   #4
Part of the Clover Leaf
u speculate right. you can wipe out your compressor.
hvac5646 is offline   Reply With Quote
The Following User Says Thank You to hvac5646 For This Useful Post:
rwfegley (01-13-2012)
Old 01-13-2012, 01:13 AM   #5
Thank you!
Old 01-13-2012, 07:36 AM   #6
HVAC Tech/ Browns Fan
Take care of them after Japan earthquake part are hard to get and cost more. The building was gone due to earthquake.
Tator1076 is offline   Reply With Quote
The Following User Says Thank You to Tator1076 For This Useful Post:
Old 01-13-2012, 07:37 AM   #7
I'm still waiting on a compressor for a customer since July.
Old 01-13-2012, 07:32 PM   #8
I just measured the pressure in the gas line at the compressor. The system was working in heat mode at maximum settings. The pressure was 450 psi which corresponds to a temperature of 130 F for R 410a. The ambient temperature was 60F. I don't know if this is excessive pressure?
Does anybody know if this is excessive for a Mitsubishi compressor?
Thanks,
Ron
Old 01-14-2012, 01:07 AM   #9
Forgot that this compressor is run by an inverter. It may not develop overly high pressures. I don't know.
Old 01-14-2012, 10:22 AM   #10
Sounds like that evap is overloaded.
Could be wrong ....don't know if your unit can gear down to handle so low a load.
But at 60* OD ambient the high side seems high. What was your indoor tmp?
Old 01-14-2012, 01:07 PM   #11
Indoor temp was 70F.