Mcquay Rps 30 Applied Rooftop Unit Fan Fail Alarm - HVAC - DIY Chatroom Home Improvement Forum
Old 04-05-2011, 11:20 AM   #1
mcquay rps 30 applied rooftop unit fan fail alarm
any ideas about a fan fail alarm. saf is fine and the air tubes are not clogged and attached properly.
c.gould is offline   Reply With Quote
Old 04-05-2011, 02:08 PM   #2
Rewards Points: 1,216
Need a lot more info than that. Could be a lot of things causing it.
COLDIRON is offline   Reply With Quote
Old 04-05-2011, 02:23 PM   #3
what other info would you need, srry still fairly new in the field. Only thing opperating on the rtu's are the return and supply fans, we cave electric heat in the vavs throughout the building.
Old 04-05-2011, 03:56 PM   #4
Look at the electrical drawings and see what would cause the fan fail circuit alarms, go from there. Keep it simple.
Old 04-05-2011, 08:17 PM   #5
Fan fail is caused from the air flow switch opening. What controller does this have mt2 or 3? I think fan fail needs to occur 3 times within 24 hours for it to shut off and need a manual reset. So it might have happened once and tried to come back on and it did if both fans are currently running.
Hubcap626 is offline   Reply With Quote
Old 04-06-2011, 07:22 AM   #6
It does try 3 times then goes into alarm and shuts down. It is m2 applied rooftop unit controller
Old 04-06-2011, 09:03 AM   #7
Bad air flow switch. Open up door at supply fan and jump out normally open contacts on pc7, the airflow switch. Turn on unit and see if it stays on. Or just put wires on normally closed contacts until you can get a new airflow switch.
The Following User Says Thank You to Hubcap626 For This Useful Post:
c.gould (04-06-2011)
Can't get unit to turn on need electrical help please-wiring diagram included igotshocked Electrical 33 01-30-2014 06:13 AM
Ruud Pack unit "KABOOMS" upon First Light Up of the Day! Wirenut2tite HVAC 18 12-15-2012 11:11 AM
AC condensing unit failure? Hotinsummer HVAC 3 08-09-2009 03:08 PM
Trane Rooftop Unit junior40 HVAC 1 11-03-2008 05:22 PM
central unit will not come on ....please help guyasc HVAC 5 08-24-2008 06:10 PM