Manual J Calculation… What Does The Resulting BTU Value Mean? - HVAC - DIY Chatroom Home Improvement Forum
Old 05-23-2014, 09:54 AM   #1
Rewards Points: 113
Manual J calculation… what does the resulting BTU value mean?
Let's say I do or have done a Manual J HVAC load calculation for my house and it says I need such-and-such number of BTUs for heating and cooling. Are that value the actual numbers of BTUs that must be supplied per hour to keep the temperature at the desired level, or is that the BTU output of the heating and cooling appliance I should be shooting for? It doesn't seem like it should be both because then the appliances would be running 24/7…
iLikeDirt is offline   Reply With Quote
Old 05-23-2014, 03:55 PM   #2
Rewards Points: 222
when you do a manual J it will tell you how much heat and ac you need for each room. add those up and you get the total for the house and then you size that total with the equipment. There is a national chart called a MEAN TEMP. guild that will let you know the average temp. for each city in the US. Where I'm at its 85 degrees F. in the summer and 15 degrees F. in the winter. They use these numbers to size the system.
hvac instructor is offline   Reply With Quote
Old 05-23-2014, 04:42 PM   #3
An old Tradesmen
Rewards Points: 6,584
It should be both.
A properly sized A/C and or furnace should run 24/7 at design conditions. Which only happen a few hours a year compared to the normal average temps.
Old 05-23-2014, 04:47 PM   #4
Rewards Points: 113
Originally Posted by beenthere View Post
It should be both.
Ah, that makes sense, since the design conditions are "worst-case scenario" ones.
Old 05-23-2014, 06:15 PM   #5
HVAC Tech/Owner
Rewards Points: 430
Design conditions are not worst case. Just about a 2% of
Technow is online now   Reply With Quote
Old 05-26-2014, 01:44 PM   #6
Rewards Points: 310
Design conditions are based on lowest and highest average temps for your area based on about a 10 year average, and then calculated based on about a 98% of the time model so for approx. 2% of the time you may have actual heat gains or losses that exceed your equipment sizing requirement, so you may be a little hotter than you would like, or a little cooler than you would like on those "worst case" days
HVACDave is offline   Reply With Quote
wiring a manual transfer switch properly mikerr Electrical 13 03-26-2014 06:24 AM
Credibility and reality of a manual J Missouri Bound HVAC 12 06-15-2012 09:32 PM
Manual D Friction Rate Worksheet kilosos2 HVAC 38 01-11-2011 05:36 PM
Manual transfer switch to power an existing sub-panel joestewart Electrical 10 11-23-2009 03:30 PM
Thermostat from Manual to Digital trinamillersmit HVAC 5 07-02-2009 10:21 AM