#1 |
Manual D Friction Rate Worksheet
Hey guys
I bought the Manual D book so I can redo all my ductworks in my home. I read alot of stuff in the Manual D and some I understood and some just went over my head. I finally figured out I need to first find the friction rate before I can properly size the trucklines. I have a few questions about the worksheet. 1. In the component pressure losses (CPL) some of the values are given in the manual D book in form of a chart. If I cant find the exact values of my current system should I use some of those values? Like example the Electric resistance heating coil,j I put .13 iwc cause on the chart figure 6-3 in the manual D book, it has 1200 cfm at .13 iwc . My blower on heating mode is set for 1200 cfm. 2. Should I have a value for the "Direct expansion refrigerant coil" in the component pressure losses (CPL)? I have A shaped coils. I dont know whats the IWC for them.The coils I got are ASPEN CE48D44-210-020 R410. Should I also use the default values set in Figure 4.2 in Manual D book. 3. I am planning to put 3 manual dampers. So when I put that into the CPL list I should put 0.03 x 3 =0.09 ? Again 0.03 is a value I got from manual D. I looked up the dampers online listing and it said it can withstand max pressure differential up to 1.0 WC. 4. When calculating the Total Effective length (TEL) it should be only the total trunklines lengths, correct? I dont include the plenum length? I am planning to use R-6 ductboards. 5. If you guys need to know my ESP for my air handler is '0.5 esp ,tested without filter installed, dry coil condition' thats what the manual for the air handler says . AIr handlers is a York MV16CN21H set at 4 ton 1600cfm. Let me know if I am on the money! lol |
#2 | |
An old Tradesmen
Manual D Friction Rate WorksheetQuote:
#3 |
In the manual all it says that " Airflow at nominal voltage , bottom return at 0.5 ESP, tested without filter installed, dry coil condition." It says this below the Airflow charts but the charts don't have a listing of static pressure at each cfm.
There is also a chart in the manual about the heater kits and it lists the max static pressure is .5. Here's a link to my manual http://www.luxaire.com/PDFFiles/255143-UIM-G-1208.pdf page 10 Table 9 list the heater kit...I got a 10KW heater strip and page 11 Table 15 list the different CFM settings, below the Table is some notes and Note #1 says about the .5 ESP. So I dont know if I need to maybe contact York about the issue. I can also get a manometer as I have a fieldpiece hvac tool and it has a add-on manometer I can attach to check static pressure. If you think I can acquire the esp like that. |
#4 |
An old Tradesmen
The foot notes say it will move set CFM up to an ESP of .6".
After that, the CFM is reduced byn 2% for each .1" above .6". Contact Aspen for teh PS of your coil at what ever CFM your going to be using. You need the manual for the strip heater kit. that should have the PD of it listed. Also, 10 KW for a 4 ton blower? Gonna have some cool feeling air coming from it. What size is the outdoor unit? If you have the heat kit model number. I may have its PD at what ever CFMs. |
#5 |
I have a 18 seer 2 stage York Affinity 8T system. Outside Unit is a Czh04811B and inside Air handler is A Mv16cn21H. A 4- ton unit. For heating I have the airflow set at 1248 cfm. The air that comes out isnt that hot but it does work.
I really dont know which heating kit is installed but I know its a 10 KW as the installers wrote on the Air handler "10 KW heat". And if its the original heating kit from York then based off the manual it should be the 4hk16501506. Let me see if I can open the air handler and see if I see any label or anything on the heating strips. |
#6 |
An old Tradesmen
1248 is a bit low for that unit in heat mode.
I don't have that heater's data. but, it should only be a .03 to .07 PD. 10 KW at 1248 is only a 25 degree temp rise. So your defrost air temp is going to feel cool. You shouldn't need to have the CFM that low to get a nice warm discharge air temp from that heat pump. |
#7 |
Ok, I opened my unit and found the label for the heating strip.
It says "Warren Technology" Integral Limit Control Model: W4k1002B 9.60-10.00x5.50 240 Volt 1PH 2Step 60hz 40.00 amps 1009 9600 watts s/nXXXXXXX Similar To: 4HK16501006A Thats all the label says. 4HK16501006A is the yorks heating kit and in the manual it says its a 7.2 KW. Although this one is a 9.6kw . The Warren technology company has its address on the label. Its a local company in my area. I will see if I can contact them. You see anything there that we can use to extract the SP? .. oh I found the heater online ... check out http://www.theacoutlet.com/10KWYORKSTRIPHEAT.htm Last edited by kilosos2; 12-18-2010 at 03:36 PM. |
#8 | |
I dont have a heat pump system! Its only electric heat strip. I am in miami , fl. I used it last week when it got down to the 30's . It works but it doesn't have a nice hot airflow like in my dad's house or other peoples homes I have visited. But it does work to raise the temp up. I think the cfm should be put at 1468 cfm( Tap C on the comfort trek control board) as one person told me on another forum. Last edited by kilosos2; 12-18-2010 at 03:33 PM. |
#9 |
An old Tradesmen
It doesn't list actual specs for it. but its no more then a .07" PD.
Since its only electric strip heat, you can drop it to 100 CFM and have a temp rise of 31 degrees. That heat kit is used in 1.5 ton units that only move 600 CFM, so no problem. |
#10 |
Whoa your saying the 10kw is for a 1.5ton unit that uses 600 cfm? The lowest cfm setting I can use is 1248cfm. I guess I will leave it at that. I will call york and see if they can give me any PD values. I will also use the .07 pd for this electric strip.
Lol- Here goes my thread off topic. Beenthere as I was looking inside the air handler and looking at the control board terminals. I saw the W1 and W2 terminals bridged with a small piece of tstat wire. And then I have another wire that is connected to the W2 terminal on the control board and that wire hooks up to my IAQ EIM-W1 terminal. Is that correct or I should remove the bridge and it should be 2 separate wires going like W1 from control board to W1 on IAQ EIM W2 from control board to W2 on IAQ EIM ?? Last edited by kilosos2; 12-18-2010 at 04:29 PM. |
#11 |
An old Tradesmen
Its seldom used in anything larger then a 2.5 ton.
| The Following User Says Thank You to beenthere For This Useful Post: | kilosos2 (12-18-2010) |
#12 |
I dont know if you saw my edit of the post above about the terminals. Let me know what you think if that is correct or not.
Anyways thanks so much for your help. I'll keep you posted on my outcome! Last edited by kilosos2; 12-18-2010 at 04:41 PM. |
#13 |
An old Tradesmen
Your wiring is correct.
#14 |
Manual D Friction Rate Worksheet |
#15 |
Hey beenthere
Ok I got all the values down from ASPEN for the coil and Warran for the heating strip. I got a friction rate of 0.0384615. ( my ASP was ESP .5 - CPL .48 = 0.02) (FR= 0.02 ASP x 100 / 52 TEL= 0.0384615) I rounded it up to 0.04 . You think that sounds right? Last edited by kilosos2; 12-20-2010 at 03:18 PM. |
| Display Modes | |
| Manual transfer switch to power an existing sub-panel | joestewart | Electrical | 10 | 11-23-2009 03:30 PM |
| Thermostat from Manual to Digital | trinamillersmit | HVAC | 5 | 07-02-2009 10:21 AM |
| Drop Rate on Scott's Drop Spreader | SPS-1 | Landscaping & Lawn Care | 1 | 04-28-2009 09:24 PM |
| Toro 7/24 Snowblower - friction wheel | Ottawa | Landscaping & Lawn Care | 1 | 02-02-2009 09:01 AM |
| needing manual | HandyMac | Landscaping & Lawn Care | 2 | 07-03-2008 03:26 PM |