Low Suction/low Head Pressures - HVAC - DIY Chatroom Home Improvement Forum
Old 05-19-2011, 02:26 PM   #1
Low suction/low head pressures
Hi,
I'm having problems with a 3t HP. My suction is running at 45psi and head is at 110psi. I checked evap coil and filter and both were clean, so I figured it was low on R22. I added 7 lbs. (factory charge is 7.25 lbs) and pressures did not change. The suction line is frosting up to the compressor. I'm starting to think I have a bad reversing valve. Any help will be great. Thanks
DougEFresh is offline   Reply With Quote
Old 05-19-2011, 05:04 PM   #2
AKA HVACTECHFW
Rewards Points: 1,208
have your tried switching the reversing valve to see if it switches? what are your temps entering and leaving the reversing valve? Where are you hooking your gauges up at?
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 05-19-2011, 05:35 PM   #3
An old Tradesmen
Rewards Points: 6,598
At those pressures, its not a reversing valve problem.
Switch it to heat mode, I bet the head pressure sky rockets.
Old 05-19-2011, 09:06 PM   #4
Is that your discharge or liquid you are reading? The 110
Hubcap626 is offline   Reply With Quote
Old 05-19-2011, 09:26 PM   #5
Yes I powered the reversing valve 3 or 4 times, thouht it would loosen up if it was stuck part way, and yes the head pressure went up. The 110 psi was on the discharge side.
Old 05-19-2011, 09:32 PM   #6
An old Tradesmen
It isn't the RV.
You have a restriction elsewhere.
The Following User Says Thank You to beenthere For This Useful Post:
DougEFresh (05-19-2011)
Old 05-19-2011, 09:50 PM   #7
Thanks, I'll look deeper into it.
Old 11-15-2012, 05:26 PM   #8
Refrigerant restriction
beenthere: Where would I find the restriction, most likely? I have a HP with same problem as the other guy. I took the piston metering device off and it looks good. Shouldn't I have another metering device? Would it be at the evap, connected to the dist tubes?
plangill is offline   Reply With Quote
Old 11-15-2012, 05:29 PM   #9
I also had the same prob on another unit and the TXV powerhead lost charge. Replaced and fine. This unit has no TXV.
Clipped Head v. Full Round Head Nails RickT Carpentry 10 11-18-2010 10:00 AM
Handheld shower in addition to fixed head OnTheGo Plumbing 4 03-25-2010 12:31 AM
Shower Head Breaking Off mbarnes Plumbing 3 01-11-2009 07:38 PM
Weird shower head leaking problem shawnst Plumbing 5 12-25-2008 12:23 PM
Weak stream of water from shower head. SuperAkuma Plumbing 3 08-01-2008 06:49 PM