Old 10-25-2009, 11:48 PM   #1
Default low domestic hot water flow with tankless coil
Hi, I have been investigating a hot water issue at my house and I think I have it figured but I wanted to ask around before I start cutting pipes.
I have an oil burning furnace with a domestic hot water coil, and water baseboard heat. The problem I've been having is lack of hot water in my fixtures all year 'round. Specifically, water temperature is very hot, but the flow is terrible. This is true of all fixtures (showers, faucets, washing machine, etc). This is not unbearable, because I can simply increase the oil furnace temperature and adjust the cold water faucet to reach the desired output temperature. It does make showers unpredictable, however, because very slight pressure changes DRASTICALLY affect water temperature. The large flow difference betwen hot and cold also means that adjusting the cold knob to the right temp is very difficult as the slightest turn bounces between hot and cold extremes.
I checked the manual for the furnace, it says that the model I have is rated to heat 3.25gpm of 40F water to 140F with a 200F internal boiler temperature. According to my well pressure tank gauge, the cold water pressure is at 43psi. The furnace's max cold water supply pressure is 50psi. I measured the flow rates manually with buckets from the very first fixture on the line. The cold water was flowing at over 5gpm, but the hot water only about three quarts in a minute.
I have hard water so my guess is that the hot water pipe, or the cold water pipe that leads to the furnace, is partially blocked or clogged up with scale. There are some old corroded compression valves in there, too. I was going to start replacing pipes and valves until flow improves, but I want to make sure I am not just wasting my time.
Shouldn't the hot and cold water pressures be about the same? Both lines are entirely 1/2" copper pipe from the well pressure tank onward. If the manual says it can do 3.25gpm at 50psi, shouldn't I be getting nearly that at 43psi? Certainly at least 1-2gpm.
By the way the furnace is 2yrs old so I doubt it is at fault unless it has a valve somewhere that isn't fully open. This issue existed since it was installed, which was when I bought the place, as the old one was failing.
mike42 is offline   Reply With Quote
Old 10-26-2009, 03:42 AM   #2
Great info! Really informative. It is helpful for me.
Cheap tennis ball machine information and reviews of prince and tennis twist | Lobster tennis ball machine
madvimjum is offline   Reply With Quote
Old 10-26-2009, 05:50 AM   #3
An old Tradesmen
The tankless coil is restricting.
Also. You should have a flow control valve, and a mixing/tempering(code requirement) valve on the hot water line from the coil.
Old 10-26-2009, 12:22 PM   #4
Are you suggesting that it is restricting by design, or because it is improperly tuned or damaged somehow? If it's rated at 3.25 gallons per minute, shouldn't I get something close to that? I'm getting well under 1gpm.
Should I call the boiler installer or this just "how it is" with this kind of system. This is my first home and first oil furnace so I do not know what is normal.
Old 10-26-2009, 12:24 PM   #5
There is a compression valve on the hot water line coming out of the boiler, and it is fully open though it looks very old. I'm not sure what a mixing valve looks like, I'll have to look it up. It should be up to code as it was installed in 2007.
Old 10-26-2009, 01:28 PM   #6
I don't think I have a tempering valve. There isn't anything external to the boiler mixing the hot and cold pipes as shown here: http://www.inspect-ny.com/heat/MixingValves.htm
Either it isn't a code requirement in my area or I got screwed over and will have to install it myself.
Old 10-26-2009, 03:51 PM   #7
An old Tradesmen
The tankless coil is soimewhat restrictive by design. But as mineral build up occurs. It becomes more restrictive.
So it could need cleaned out.
Also look for a device that almost looks like a coupling on the copper line that feeds water to the coil. It may have a flow control device on it. That restricts how much water you get through your coil.
Although they are usually sized close to what your coil rating is.
Code has required a mixing valve long before 2007.
Your coil most likely needs cleaned/cooked out.
Old 10-26-2009, 05:34 PM   #8
I definitely don't see a mixing valve anywhere on there. I just went out and bought one for $30, I'll have to install it.
As for the restrictive coils... is it reasonable for me to expect something near the 3.25gpm rating? I don't think corrosion/building in the coil could be the issue as it has pretty much been this way since it was installed. The inlet compression valves are all open. too, though they *are* really corroded as they were not replaced when the unit was installed.
Old 10-26-2009, 05:36 PM   #9
An old Tradesmen
If you have the water pressure. Yes, you can expect 3.25GPM. What is your water pressure.
Old 10-26-2009, 05:52 PM   #10
The cold water pressure is 40-45psi ~20ft from the boiler, all 1/2" copper. The boiler says max cold input is 50psi, and its rated for 3.25 gpm hot output. I'm only getting .69gpm of hot water output, something must be severely restricting flow.
It looks like a tempering valve will "fix" the issue, but really I think it will just hide it.
Old 10-26-2009, 05:54 PM   #11
Thank you for the advice, by the way. I'm somewhat nearby, Norristown/King of Prussia area.
Old 10-26-2009, 06:21 PM   #12
An old Tradesmen
About 45 minutes to an hour a way. Depending on traffic.
I would disconnect one of the valves bore the coil. And see if its getting good pressure. And then take one apart after the coil. And see if the pressure is the same.
If its not, something may have got in teh coil when they installed the boiler.
Old 10-28-2009, 03:35 PM   #13
My buddy and I started taking off valves and cutting/rejoining the suspect sections of pipe yesterday. Nothing was found, the boiler itself is definitely the bottleneck. The cold water pipe has good pressure all the way to the domestic coil input, and the pressure of the water coming directly out of the domestic coil output pipe is very poor. I am going to call the boiler installers to find out why I'm not getting the rated capacity, and why no tempering valve was installed if that is a code requirement.
Old 10-28-2009, 03:37 PM   #14
Can you give me any more info about the code specification that requires mixing/tempering valves? I know of, for example, the national electric code, which is referenced by local governments, but I do know of a plumbing equivalent.
Old 10-28-2009, 04:01 PM   #15
An old Tradesmen
IMC 1002.2.2.2 Scald protection.
Where a combination potable water heater and space heating system requires water for space heating at temperatures above 140°F (60°C ), a tempering valve shall be provided to temper the water supplied to the potable hot water distribution system to a temperature of of 140°F(60°C) or less.
More On This Topic
Hey everybody, Don Golden for Expert Village and let's move on with the shower project. We've just taken off the valve and now I want to show you the real crucks of our problem is right here. This is called your water cartridge and this is right here, is... Read More »
If you live in a part of the country where the temperature gets down below freezing, you just might run into the problem of having your water or drain pipes freeze. As long as you’re home (and not off vacationing somewhere warm) you can usually fix... Read More »
Ok. Now, we're going to talk about how we ran cold water. Again, our cold water line was already existing here. So, I cut off the old pipe added a ninety. And, we've started running it along the wall here. And, then here we have a "T" that runs up and... Read More »
Hi! I’m Jim McKelvey with Third Degree Glass Factory in St. Louis. You can check us out on the web at www.stlglass.com. Today, we’re going to learn about glassblowing for expertvillage.com. One of the secrets to making really nice glass is... Read More »
Hi! This is John on behalf of Expert Village. In this video clip, I will show you step 1 for installing a ball valve. I am going to be installing a ball valve on this pipe. This pipe is a hot water pipe, and I know that because when I trace it back, it... Read More »
Need help with domestic hot water zone... GerryL HVAC 0 05-10-2009 09:09 AM
Testing 12 year old hot water expansion tank? DJfixer Plumbing 2 01-01-2009 10:09 AM
Hot water pipe making scary noises - Please help!!! Sarah24 Plumbing 4 12-16-2008 12:24 PM
Is 1/2 Pex more restrictive than 1/2 copper? twilightcall Plumbing 19 06-24-2008 09:32 AM
Tankless Water Heaters Recalled for Repair Due to Carbon Monoxide shimp Plumbing 1 01-22-2008 08:52 PM
Copyright ©2000 - 2009, Jelsoft Enterprises Ltd.