Old 03-22-2011, 07:31 PM   #1
load explosion when new furnace ignites
We have had a new EVEREST EXTREME COMFORT furnace installed 01/20/11. Since it has been installed it has a banging every time it ignites. I was told...that is the way it is ! MODEL GHM950904CX
SERIAL # 1003413560
There is someting not correct for this to happen !
Thanks in Advance !
Ken
Ken Sorenson is offline   Reply With Quote
Old 03-22-2011, 09:36 PM   #2
#1 HAWKEYE FAN
hardwareman's Avatar
you should move this over to the HVAC section, but it sounds to me like the plenum is probably expanding when the fan kicks on causing a banging noise. Not normal and is fixable
................."I want a house that has gotten over all its troubles. I dont' want to spend the rest of life bringing up a young and inexperienced house"...........
hardwareman is offline   Reply With Quote
Old 03-22-2011, 10:43 PM   #3
HVAC / Plumbing
Either sheet metal duct work popping or something isn't lined up correctly .Ie, burners, ignitor or both..
Like hardwareman said............. It Ain't normal
kenmac is offline   Reply With Quote
Old 07-20-2011, 07:10 PM   #4
If you still have the banging on ignition, check for a restriction in the exhaust piping. Long lengths should be increased from 2" to 3". Some installers make the mistake of putting the intake screen on the exhaust also. A quick check to see if you have an exhaust restriction; shut the furnace off, remove the door covering the gas valve and burners, turn the furnace on. This eliminates any back pressure. If it ignites smoothly, you have a restriction.
P. Boots &Sons is offline   Reply With Quote
Old 07-20-2011, 09:02 PM   #5
30 year tech
hvac122's Avatar
The pressure switch would not let it come on with backpressure.
First you need to find out if the bang happens on ignition or when the fan comes on. Then we can narrow down what's going on.
hvac122 is offline   Reply With Quote
Old 07-20-2011, 09:34 PM   #6
Yes a pressure switch will let this happen, the pressure switch will snap open then closed during the mini explosion during combustion. After ignition the unit usually runs fine until shut down. I have seen this several times. Actually saw one chatter on and off for 15 seconds until the exhaust flow smoothed itself out. Try it.
Carrier Infinity 69 Trouble Code 42 bodya1 HVAC 4 12-05-2010 07:43 PM
When to replace a furnace? stanlam HVAC 3 07-20-2010 08:21 PM
Have an oversized furnace turfgrass HVAC 5 02-22-2010 04:48 PM
Oil furnace does not fire up sbhavinm HVAC 5 01-17-2009 08:06 AM
Problems with new furnace..Overheating, having to reset. Furnace too big? Tommy2 HVAC 41 12-01-2008 02:55 PM