Lennox TUE080A948L3 - NO HEAT - HVAC - DIY Chatroom Home Improvement Forum
Old 11-18-2011, 08:21 AM   #1
The unit was working fine until this morning. The blower comes on to clear the flu and start a draft. Then the ligniter comes on and stays lit for about 15 seconds but the unit never lights the burners. The blower comes on an runs until I lower the thermostat below the current 59 degree temperature. The gas fire logs which run off the same gas line work fine. I turned off the power to unit for 15 / 20 minutes hoping there may be a reset. After reapplying power no change.
BLB76 is offline   Reply With Quote
Old 11-18-2011, 10:12 AM   #2
Well, to me without being there to check it with my VOM meter,I would say that its a bad gas control valve. My reasoning is that everything else is happening that should happen, the gas valve is not opening to let gas flow to ignitor and burners. Just one other thing, I have worked with Lennox products for over 30 years.....I dont recall them makeing a unit that has a TUE******* model number, sounds like a Trane to me.
harleyrider is offline   Reply With Quote
Old 11-18-2011, 10:25 AM   #3
You are exactly correct. My error - it is a Trane. This last time it cycled I tapped lightly on the gas valve and the unit came on. Any idea where I could find a Gemini Gas Valve #4033RG51G? I am in Winston-Salem, North Carolina. I called a Trane dealer early this morning and they have not responded. Thanks so very much.
Old 11-18-2011, 11:09 AM   #4
biggles's Avatar
if the valve is a standard 24V 2 wires and the pilot gas fed off it...check Grainger locally TRANE uses different brands on all their controls....and it changes year to year... put up a pix of the valve and model number off the valve.that tapping of the valve and it opens to heat could be a loose wire under the hat...shut the gas and unsrcew the top of the valve so you see the wire connection within.if you have a ohm meter shut 115V service switch OFF...connect it to the 2-24V spades on top of the valve and see if you get a bouncing on the meter as you move the wires...a loose soldered connection or pinched wire.... http://www.bestbuyheatingandaircondi..._Code=gv-trane
Lennox Heat Pump shuts down sully2 HVAC 47 08-19-2011 09:56 PM
Using Gas heat during Defrost mgroves HVAC 15 12-18-2010 05:51 PM
Lennox heat pump m/n 10acb42-11p rkhayes HVAC 3 07-25-2010 08:07 AM
Lennox xp15 heat pump, power outage blip GEAF HVAC 4 04-02-2010 05:10 PM
Heat Pump Blower always on gg_daman HVAC 1 12-16-2009 06:15 AM