Lennox HVAC Circuit Board Problem - HVAC - DIY Chatroom Home Improvement Forum
Old 09-11-2013, 10:25 AM   #1
Question
Lennox HVAC Circuit board problem
I have a Lennox central unit with a 24L8501 circuit board that is flashing alternating fast lights. When I bypass it the blower goes on. There is 120 V getting to the board. The compressor is working.the model is G26Q4/5-100-6. It looks like the board was wet at some point. My friend said replace the board. Is there anything else I can try before spending the money?
Thanks,
Joe
Joenovo is offline   Reply With Quote
Old 09-11-2013, 03:34 PM   #2
Rewards Points: 77
Here is a link to the service manual for your unit: http://0190acd.netsolhost.com/manuals/G26_Series.pdf
If you look on page 12 it shows that alternating fast flashes is:
Improper main ground or
Line voltage below 75 volts
or
Broken ignitor
or
Open ignitor circuit
Here is another link that contains a schematic for your board (page 10):
http://www.acfurnaceparts.com/Servic.../Surelight.pdf
If you look at the schematic on page 10 (bottom right) it shows the main grounding point. That is where I would start be inspecting the ground and making sure it is tight and not corroded. Turn off power to unit before tightening any wires or screws as a safety precaution!
Do you have a condensate drain safety switch that might be preventing blower from coming on?
firedawgsatx is offline   Reply With Quote
Tags
lennox 24l8501
Dimming lights on one circuit, GFCI breaker tripped boatman537 Electrical 4 06-05-2012 10:43 AM
HVAC condensor fan outside intermittant wheelsup HVAC 21 05-24-2012 10:25 AM
Obsolete Air Handler Circuit board dvsrikanth HVAC 3 12-03-2010 01:01 PM
Goodman Circuit board B1809913 tilphan HVAC 30 12-02-2010 06:08 PM
Inducer fan assembly or inducer control circuit board failing realblonde94526 HVAC 3 05-12-2008 07:28 PM