-   -   Lennox HVAC Circuit board problem (http://www.diychatroom.com/f17/lennox-hvac-circuit-board-problem-186833/)
Joenovo 09-11-2013 10:25 AM
I have a Lennox central unit with a 24L8501 circuit board that is flashing alternating fast lights. When I bypass it the blower goes on. There is 120 V getting to the board. The compressor is working.the model is G26Q4/5-100-6. It looks like the board was wet at some point. My friend said replace the board. Is there anything else I can try before spending the money?
Thanks,
Joe
firedawgsatx 09-11-2013 03:34 PM
Here is a link to the service manual for your unit: http://0190acd.netsolhost.com/manuals/G26_Series.pdf
If you look on page 12 it shows that alternating fast flashes is:
Improper main ground or
Line voltage below 75 volts
or
Broken ignitor
or
Open ignitor circuit
Here is another link that contains a schematic for your board (page 10):
http://www.acfurnaceparts.com/Servic.../Surelight.pdf
If you look at the schematic on page 10 (bottom right) it shows the main grounding point. That is where I would start be inspecting the ground and making sure it is tight and not corroded. Turn off power to unit before tightening any wires or screws as a safety precaution!
Do you have a condensate drain safety switch that might be preventing blower from coming on?