Checked three electric air handlers today, pole to pole and individual leg to ground, one to make sure 15 kilowatts divided my 241 volts (total of each leg to ground) equated to 62.2 amps. Two legs of 120 on 4 awg wire (which is rated to 75 amps) each leg to a 70 amp Square D double pole breaker that was tripping in heating mode.
Guss what the problem was? Yup, they need an electrician, bad breaker.
Doc Holliday is offline   Reply With Quote
Old 11-29-2011, 09:05 PM   #17
Lennox G26 Furnace
Thank you for being patient with this greenhorn. I'll check again. I borrowed this multimeter and not sure how to set it. It is a radio shack auto-range digital. I have it set to volts. If I place this in a regular outlet I get (.300v) I'm running down to check again
bucks454 is offline   Reply With Quote
Old 11-29-2011, 09:09 PM   #18
Lennox G26 Furnace
you should see 120 volts give or take a few......makes me wonder if you have it on VDC instead of VAC ?
harleyrider is offline   Reply With Quote
Old 11-29-2011, 09:14 PM   #19
Lennox G26 Furnace
I think you have it on milivolts. It should be on Volts Alternating Current, VAC.
Old 11-29-2011, 09:16 PM   #20
Lennox G26 Furnace
If L1 is load and L2 is line then I get (.630v)
Old 11-29-2011, 09:23 PM   #21
Lennox G26 Furnace
LOL....no, L1 is LINE HOT L2 is neutral, doc and i both feel that you don't not have the meter set on the proper scale. when you put the two leads into a wall plug using the two slots ( l l ) you should see 120 give or take on your meter.
Old 11-29-2011, 09:28 PM   #22
Lennox G26 Furnace
I think I've figured out how this meter gets to VAC. At least now I am hitting 120 on a regular outlet. L1 and L2 read 163v. That is if L1 is line in and L2 is load out.
Old 11-29-2011, 09:59 PM   #23
Lennox G26 Furnace
Just to explain what i see. The top of the transformer is marked "line" with two larger contacts. And "load" which has two smaller contacts.
Old 11-29-2011, 10:15 PM   #24
Lennox G26 Furnace
what does the line voltage measure....put meter on two terminals marked line, also what dose voltage measure on load?
Old 12-04-2011, 06:02 PM   #25
Lennox G26 Furnace
Follow up to my issue: Cutoff switch had a short, not allowing power into the furnace. This was found by 1) Digging out my multimeter I know how to run and giving back the digital one that was giving odd measurements. 2) Testing output at breaker which was 120v, then checked the input at the cutoff switch. I was surprised the connections were not wrapped in electrical tape. I measured 120v on the incomming wires so easy to assume the wire was good. I reconnected the wires, wrapped the switch with tape and put it back together and prayed it would fire. It did.
Old 12-04-2011, 06:14 PM   #26
Lennox G26 Furnace
Thank you to Harleyrider, Doc Holliday, and Marty for your replies. What I've learned from this: Use the right tools that you know how to use, when it comes to power issues start from the source and work your way out. Now I have a few extra parts in case they fail in the future.
Old 12-04-2011, 06:17 PM   #27
Lennox G26 Furnace
yw
Tags
furnace control board, lennox, transformer no load
Possible Lennox Furnace ignitor problem Paulg1 HVAC 4 11-26-2010 05:38 PM
Lennox Furnace Model #: 90UGFA3-75-6 GauravJ HVAC 3 10-30-2010 09:24 PM
Lennox Furnace Model #: 90UGFA3-75-6 GauravJ Electrical 0 10-29-2010 07:52 PM
Lennox ghr26 furnace problems wayfis HVAC 8 01-05-2010 06:51 PM
Lennox G11Q3E-110V-6 gas furnace neato5oh HVAC 1 10-07-2006 07:43 PM