Old 11-12-2012, 11:55 PM   #1
Lennox G20R wont start
I have a Lennox G20R whisper heat furnace. It is failing to turn on.
I checked the fuse (the fustat fuse and the in-panel fuse). They are both good.
I checked to see if there is 24VAC between R&C - I measure 0V.
There is no clicking or sound when i turn on the unit. The damper door does not even open.
I recently changed the batteries on the controller unit and made sure the unit was working - that was about 3 weeks back (a regular yearly maintenance). The furnace worked after I replaced the batteries.
Any guidance here is appreciated.
Thanks,
-L
lucky66 is offline   Reply With Quote
Old 11-13-2012, 12:07 AM   #2
how
Confirm supply voltage..Does the thermostat have a fan on switch or do you have a meter to confirm supply voltage?
Remove the stat wire in the furnace connected to "R". Put a jumper between R & W to bypass the thermostat circuit.
If you have supply voltage and have jumpered the stat circuit..is the motor that operates the vent door receiving 24V?
how is offline   Reply With Quote
Old 11-13-2012, 01:09 AM   #3
I have a DMM to measure the voltage.
Thermostat has a switch.
I jumpered the stat wires as mentioned. Can you help me on how to check if the motor is receiving 24 VAC? I do not see leads at the motor.
Thanks,
Old 11-13-2012, 01:23 AM   #4
how
Did the thermostat fan switch turn on your furnace blower fan?
or
Do you know if the furnace is getting 120V?
I am not sure from your posts if you've measured any power, be it 24V or 120V in the furnace.
Old 11-13-2012, 07:24 AM   #5
door has to open to 1st before ignition...check for 24 volts to motor on door ...ben sr
Old 11-13-2012, 10:20 AM   #6
Thanks Ben Sr.
I checked for 24v between R&C terminals. I'm measuring 0. How do I check at the door motor?
Regards,
Old 11-13-2012, 02:02 PM   #7
Originally Posted by lucky66 View Post
Thanks Ben Sr.
Regards,
check your transformer 1 st...120 in on blk & white...24 volt out ...ben sr
Old 11-14-2012, 12:19 AM   #8
Checked both - I measure 0V at both locations.
I see a black spot behind the control board. I fear that something could have caused this to burn. Any advice on this?
As insurance, I have ordered a new control board.
Appreciate inouts.
The Following User Says Thank You to lucky66 For This Useful Post:
ben's plumbing (11-14-2012)
Old 11-14-2012, 07:21 PM   #9
No voltage means the fuse/breaker is blown. The burned out control board would be why.
The Following User Says Thank You to Marty S. For This Useful Post:
Old 11-14-2012, 07:25 PM   #10
Hvac Pro
AHH the good ole BCC board. Changed many of them and they get pretty roasted on the back when the fan relay blows.
The Following User Says Thank You to yuri For This Useful Post:
Air Compressor blowing start capacitors? BBC3 Electrical 9 04-28-2013 12:34 PM
Where to start laying Allure Ultra Saltyeskimo Flooring 0 09-28-2012 07:50 PM
Lennox AC won't start kcd1803 HVAC 5 08-03-2012 11:03 PM
Lennox HS29-024-2P Central Air Unit doesn't start Help!!! HVAC 9 06-13-2012 08:25 PM