-   -   lennox furnace wont stay lit (http://www.diychatroom.com/f17/lennox-furnace-wont-stay-lit-169116/)
adamsqh 01-14-2013 03:53 PM
I have a model lf24 that runs for about 2-3 min then shuts down and starts over will not stay lit though the fan blows constantly.I have changed the heat sensor the flame sensor the board the gas valve. The first time it comes on it runs for about 2.5min then as it warms up it gets down to running only about 30 sec any ideas?
danpik 01-14-2013 04:18 PM
Well, since you have changed out almost everything accept possibly the high limit or the filter I would start there. Sounds like the furnace is shutting down on overtemp. How is the airflow in and out of the furnace?
Marty S. 01-14-2013 08:25 PM
About all you have left is inducer and pressure switch.
64pvolvo1800 01-15-2013 06:33 AM
Sounds like a tired gas valve to me. Throw a voltmeter on the GV leads and see what comes first; loss of fire or loss of voltage. If voltage stays then your GV is at fault. Voltage goes first, then maybe overheat sensor?
adamsqh 01-15-2013 11:02 AM
Ok I changed the high limit and the pressure switch and got good air flow through he vent and still wont stay on and it wont give me a blinking code it blinks everything normal. Im getting ready to swap the whole thing out.
64pvolvo1800 01-15-2013 11:05 AM
Gas valve test.?
adamsqh 01-15-2013 11:07 AM
didnt check voltage on gv just changed it.
how 01-15-2013 11:12 AM
If your gas valve is shutting off without a code on the board either the
thermostat circuit is being interupted (pigtail R & W on the furnace) or the board is bad.
adamsqh 01-15-2013 11:18 AM
Ok I changed the board already but have not changed the thermostat I wired it constant so it should have ran nonstop and it still shut down.
how 01-15-2013 11:45 AM
Jumpering R & W where the stat wires connect to the furnace eliminates the chance its a partial break in the thermostat line. Make sure to disconnect the stat wires before you jump R to W.
A faulty thermostat circuit won't get picked up by the board diagnostics. Beyond that, the board should be giving you a fault led reading.
adamsqh 01-15-2013 11:58 AM
ok I just replaced the stat and still no bueno I am at a loss I think I am going to have to change the unit out with another one that I have if no other sugestions.
adamsqh 01-15-2013 12:00 PM
could it be that im not getting enough gas pressure?
how 01-15-2013 04:54 PM
Pigtail the R & W stat wire connections inside the furnace, Not at the thermostat. Turn off furnace power/ detach stat wires from R & W inside the furnace/ connect a wire between the R & W/ put furnace doors back in place/ turn power back on.
If it still shuts itself off...Thermostat circuit is OK but Board is suspect!
If it runs continuously...thermostat wiring or thermostat is the problem.
adamsqh 01-15-2013 05:21 PM
Thanks for all the advise i found out the inducer vent that goes to the pressure switch was plugged. Thanks
how 01-15-2013 06:39 PM
Hey adamsqh
I hope all is now well.
Anyone have an idea why the board diagnostic led didn't give a code for a pressure switch shut down?