How do you test the heater?
wayne1178 is offline   Reply With Quote
Old 04-28-2011, 03:34 PM   #2
JJboy's Avatar
You can test like resistor. If you heat the thermistor to the specified temperature the sensor will open the circuit.
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead.
JJboy is offline   Reply With Quote
Old 04-28-2011, 03:40 PM   #3
newtech's Avatar
Rewards Points: 164
You can ohm it, check the amp draw, and make sure you have voltage to it.
Why do you need to check it??? Problems???
newtech is offline   Reply With Quote
Old 04-28-2011, 07:05 PM   #4
If it has voltage to it, and it's not on almost 100% it's bad. Like others said check to see if it drawing amps.
Hubcap626 is offline   Reply With Quote
Old 04-28-2011, 08:22 PM   #5
I did what you suggested and it is working. My unit looked like it had a power surge. The contactor was fried and I changed that, The power to the compressor was melted and I replaced that, I check the ohms on the compress and it checks out good. What elese could it be? If I disconnect the compressor wires and force the contactor on the fan runs, When the compressor wires are connected it trips the circuit breaker. Any suggestions
Old 04-28-2011, 08:34 PM   #6
Check for continuity between the compressor terminals and one of the copper pipes. Sounds like the compressor or one of the compressor wires is shorted to ground.
Old 04-28-2011, 08:43 PM   #7
Hvac Pro
yuri's Avatar
Rewards Points: 396
MAKE ABSOLUTELY SURE that you DO NOT touch any part of the outdoor unit while testing it. If the compressor is shorted to ground and you touch the condensor YOU become the ground and could DIE.
Pay attention to this story JJ.
Old 04-28-2011, 08:54 PM   #8
Old 04-28-2011, 08:57 PM   #9
I have continuity.
Old 04-28-2011, 09:07 PM   #10
JJboy's Avatar
Now I see how this test can be dangerous. Thanks yuri for showing me this.
Old 04-28-2011, 09:09 PM   #11
JJboy's Avatar
I have continuity.
You need to replace your compressor
Old 04-28-2011, 09:52 PM   #12
An old Tradesmen
Rewards Points: 8,176
With all power OFF. And all wires removed from the compressor. When you check the compressor for continuity, check across R and C, S and C, and then R and S. R and S ohm value should equal the sum of the other 2 values.
Next, check from each of the compressor terminals to ground(one of the copper lines attached to the compressor is best), if anyone of them has continuity, the compressor is shorted to ground, and needs replaced. If n one of them do. Check that the run cap is not shorted to ground.
Its possible your compressor has a winding to winding short. That type of short can easily weld the contactor's contacts together, and heat it up enough to look like it was struck by lightening.
Old 04-28-2011, 10:15 PM   #13
Hvac Pro
yuri's Avatar
Rewards Points: 396
JJ and Wayne. BE VERY careful with a stalled/shorted compressor it can develop TREMENDOUS heat inside the compressor and literally blow the white "fusite" plug where the C/S/R terminals attach to the compressor out and you could get blasted with high pressure refrigerant/smoke/burning acidic oil/phosgene gas as it burns up. I have seen this several times and I am sure Beenthere has also. It WILL NOT give you any warning it is blowing, (sometimes makes a growling sound but not always) you DO NOT want to be anywhere near that plug or have your face near it.
Old 04-28-2011, 10:22 PM   #14
An old Tradesmen
And when it blows, if the cover isn't on, it can take a flame and the oil will come out like a blow torch was in the compressor. And if you are infront of it, you probably won't survive the burns.
Old 04-28-2011, 10:36 PM   #15
JJboy's Avatar
Just to illustrate what can happen ...... adding oil, refrigerant, etc.
Pilot on Williams millivolt wall heater goes out every 8 to 16 hours wornways HVAC 30 06-22-2011 03:29 PM
elevate electric water heater? crankbait09 Plumbing 18 04-18-2011 11:35 AM
Space Heater in Hot Water Heater Closet? MsMojoRisin Plumbing 0 02-09-2011 12:50 PM
Pressure drop across water heater, low hot water flow HVAC_NW Plumbing 2 01-17-2011 10:43 PM
Lennox Heater Light flashing Jake Spain HVAC 1 12-17-2010 09:32 PM