Lennox 80UHG Will Not Stay Lit - HVAC - DIY Chatroom Home Improvement Forum
Old 12-30-2010, 11:27 AM   #1
Lennox 80UHG will not stay lit
First thing in the morning, first time the furnace lights, all is normal. Once the house hits the desired temperature the furnace shuts off. So far, so good.
At that point the furnace will not fully relight.
The 'preignition' phase goes OK, the small blower fan starts, the burners light, run for a few seconds (varying from 5 - 30 or so) and then shut off. It will cycle through this a few times and then stop trying. Flipping the thermostat to 'OFF' and back on causes the same thing to happen again.
I've done some reading, checked the 'vacuum hose' from the small blower fan to the 'pressure sensor', no moisture at all and it works as it should if I suck on the hose end.
The two green lights on the control panel both flash repeatedly. In my reading I've seen mention of 'limit switches' which may need resetting (unless they're automatic). I've looked, I'll be darned if I can find these rascals. A description would be helpful.
Williamlane is offline   Reply With Quote
Old 12-30-2010, 12:00 PM   #2
Experienced
Jackofall1's Avatar
You might want to do a search for this, I know there have been several posts with similar issues.
Old 12-30-2010, 12:07 PM   #3
Been there, done that
Yes, there are similar threads, but with different hardware. I don't want to hijack someone else's question with my own.
Old 12-30-2010, 06:26 PM   #4
Solved
Sensor failure.
Old 12-31-2010, 11:19 PM   #5
Flame sensor
It sounds like the flame sensor. A metal rod about a 1/8" in diameter. Sets in front of the burner. Take some emory cloth or fine sand paper and clean the rod. Remove the oxidation. Should take care of the problem
semore 102 is offline   Reply With Quote
Old 01-11-2011, 11:50 PM   #6
Shefixedit18's Avatar
I had the same problem. I cleaned the flame sensor and it is working like a charm. Who knew??? I pray it continues to work. Thank you for the suggestion. You are a life saver. I will sleep warm tonight!
Shefixedit18 is offline   Reply With Quote
Lennox Furnace burner won't stay on stevea7777 HVAC 54 01-02-2016 10:38 PM
Lennox Whisper Heat burners won't stay lit Gaff519 HVAC 2 12-09-2010 12:32 PM
Lennox Gas Heater will not stay lit buddickman HVAC 1 11-23-2010 06:23 PM
Wiring Tradeline L6006C Aquastat to Lennox CBWMV Hydronic Air Handler VIPSpecialNeeds HVAC 5 03-15-2010 07:37 PM
Help with lennox furnace will not stay on. slowhand HVAC 4 12-06-2009 09:10 PM