#1 |
Lennox 80UHG doesnt blow heat
Hi...
I don't know anything about furnaces, so bare with me. Current house temp is 60 and we are freezing, can't get anyone out here asap, figured I'd drop in here to see if there are some easy fixes. I have thermostat usually always set to 66°, heaters been working fine forever, this morning I heard it click'...something starts running, but the fan never starts blowing (I dont think) nor do I hear the usually tick tick FLAMING WOOOSH sound. Any tips? |
#2 |
Look at the diagnostic lights and compare the flashes to the label on the door. Probably locked out in watchguard mode. Shut the power off, clean the flame sensor and try starting again.
#3 | |
Lennox 80UHG doesnt blow heatQuote:
Just crawled up in attic, I see 2 green LED's flashing, together, don't remember seeing a diagnostic panel, but will check again. |
#4 |
Professional
should be on the blower door, may be on inside of the door. were they flashing alternately or simultaneous? flashing fast or slow? Did you turn power off and back on? this will reset the control and may get you temporary heat. We do need the diagnostic code to help figure out the cause to come up with a repair though. It would also help if after you reset the control if you stay and watch a ignition sequence and post here what happens.... I would start with cleaning the flame sensor though.
or
IT IS WHAT IT IS To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. Last edited by hvactech126; 02-26-2011 at 12:20 PM. |
#5 |
Found the sensor, pulled out and used steel wool to clean it. Corrosion was not too bad though?
Anyways, put it back in, still same thing: the thermostat clicks some sort of action happens at the furnace, but the big blower NOR flame come on. The lights flash together with about 1-1.5 second gaps between I'd say? Heater did not work 2 years ago, guy charged me $800 for a new circuit board or something? I don't have $800 right now, let alone $8, so I was hoping for an easy fix
#6 |
i take that back on the LEDs, they are rapidly flashing, together when its trying to start. I don't know the proper startup phase so forgive my terminology. There is a humming coming from the furnace, but nothing is 'firing' nor is the big main fan blowing. I can get the fan/blower? to go if I put the thermostat to ON vs AUTO, but no heat is happening. Maybe try cleaning the sensor again? doubtful I guess.
#7 |
Professional
did you find the diagnostic legend?
that sounds like a stat problem, check for batteries, if your stat has them, then replace them. otherwise remove wires from R and W and twist together, this should change the flash at the furnace. MANUAL see page 8 for diagnostic information
IT IS WHAT IT IS To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. |
#8 | |
and 'stat' you mean thermostat on the wall right? remove wires from where? |
#9 |
Professional
Lennox 80UHG doesnt blow heat![]()
IT IS WHAT IT IS To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. Last edited by hvactech126; 02-26-2011 at 01:11 PM. |
#10 |
Both lights fast flashing means the thermostat is calling for heat. The inducer motor should come on next. Does it?
#11 |
Your image did not show.
And the diagnostic tells me everything is fine (green lights) clearly everything is not fine. |
#12 |
Like I said in the original post, I know nothing about furnaces, so I don't know what an inducer motor is. But also as I said, the thermostat 'clicks' and the furnace starts something, perhaps the inducer motor? all I know is I don't hear the usual BURNER sound NOR the big fan/blower that spits out hot air around the house. Something is turning on in furnace, just no fire or blower (blower I think is name eh? of the big fan that blows the actual hot air).
#13 |
Hvac Pro
Is the ventor fan that pushes the smoke to the chimney running. If so carefully remove the tube from the pressure switch hose where it attaches to the collector box/furnace (NOT the switch itself) and poke a paper clip/small bit thru that hole. It should be giving you a open pressure switch code but you are having a hard time reading it. Look at the pic in here
http://www.hvacparts.ca/LennoxPDF/80UHG.pdf the inducer is the fan at the top and the pressure switch is below it.
"Cut it twice and it is still too short". To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. |
#14 |
The inducer is a little motor where the flue hooks up. It comes on and closes a pressure switch if the flue is clear. Check the flue for a dead bird.
If the pressure switch doesn't close then the furnace will not continue the start up sequence. |
#15 |
Professional
Lennox 80UHG doesnt blow heat inducer.... again go to manual see page 8 for diagnostic code and below that is the sequence of operation. Page 25 starts diagnostics
IT IS WHAT IT IS To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. Last edited by hvactech126; 02-26-2011 at 01:16 PM. |
| Tags |
heater, lennox, not firing ![]() |
| Display Modes | |
| Lennox 80MGF - No Heat | Thome | HVAC | 13 | 04-02-2011 11:45 PM |
| No heat but fan constantly running for Lennox G20R03E-75-3 | sjz116688 | HVAC | 1 | 11-22-2010 07:08 AM |
| Lennox xp15 heat pump, power outage blip | GEAF | HVAC | 4 | 04-02-2010 06:10 PM |
| Wiring Tradeline L6006C Aquastat to Lennox CBWMV Hydronic Air Handler | VIPSpecialNeeds | HVAC | 5 | 03-15-2010 07:37 PM |
| Which honeywell thermostat should I buy for my Carrier heat pump? | mannypp | HVAC | 29 | 01-30-2010 03:21 PM |