Lennox 80 Heater - HVAC - DIY Chatroom Home Improvement Forum
Old 01-15-2012, 10:08 AM   #1
Lennox 80 heater
The led diagnostic pattern indicates pressure switch open how do I fix this
Aegbert is offline   Reply With Quote
Old 01-15-2012, 12:28 PM   #2
Hvac Pro
yuri's Avatar
Rewards Points: 2,266
post the complete model and serial # first.
Old 01-15-2012, 12:40 PM   #3
this "code" is simply letting you know that the pressure switch did not close. Normally when the furnace is not running the switch is what we call "normally open", when the t-stat calls for heat and the draft motor starts it pulls the pressure switch closed, this MUST happen for the ignition sequence to be completed.
Several things can keep the pressure switch from closeing.....if the ventor motor does not start, the pressure switch will not close, if the flue pipe of even the throat of the ventor is plugged the pressure switch will not close. If the proving tube (usually connected to the draft motor housing or the burner box is plugged or obstructed the pressure switch will not close.......finally and the rarest situation.......the switch its self is bad.
Typically a trained service technician will use a magnihelic Gage and or a manometer to determine the root of the problem.
harleyrider is offline   Reply With Quote
Old 01-15-2012, 05:24 PM   #4
HVAC Tech/ Browns Fan
Clean out port on Draft motor. Its on top were the orange or gray tub is going from pressure switch to port
Tator1076 is offline   Reply With Quote
Old 01-16-2012, 05:10 PM   #5
Egbert400's Avatar
I took off red hose after I shut off the unit , the tube was clogged and the opening to the motor for the pressure switch was covered in junk, I cleaned it out with a needle and hooked it back up worked fine pressure switch closed furnace works great.
Egbert400 is offline   Reply With Quote
Lennox Heater Richard Hayden HVAC 10 01-06-2012 02:32 PM
Pilot on Williams millivolt wall heater goes out every 8 to 16 hours wornways HVAC 30 06-22-2011 03:29 PM
Lennox G61 quote, also water heater and ac bw77 HVAC 1 06-16-2011 07:12 PM
Lennox Crank case heater wayne1178 HVAC 18 04-29-2011 09:05 PM
Lennox Heater Light flashing Jake Spain HVAC 1 12-17-2010 09:32 PM