Lennox 12ACB48-3P - First REAL Repair - Excited :) - HVAC - DIY Chatroom Home Improvement Forum
Old 05-28-2011, 02:49 PM   #1
JJboy's Avatar
Lennox 12ACB48-3P - First REAL repair - Excited :)
Low pressure is too low (icing suction line). First image is showing pressures with the system running. Second image the system is off after +/- 4 minutes. I am suspecting a constraint on the TXV. Please confirm
I need more info about this TXV.
EVAP MODEL: C23-51FC-1
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead.
JJboy is offline   Reply With Quote
Old 05-28-2011, 03:17 PM   #2
AKA HVACTECHFW
Rewards Points: 1,208
basics first, how does the filter, blower wheel, or evap coil look? plugged? Is the condenser plugged?
IT IS WHAT IT IS
hvactech126 is offline   Reply With Quote
Old 05-28-2011, 03:36 PM   #3
JJboy's Avatar
Everything is ok.
Old 05-28-2011, 03:40 PM   #4
AKA HVACTECHFW
remove the TXV sensing bulb and put it in Hot water. Does the head go down and suction come up?
IT IS WHAT IT IS
Old 05-28-2011, 03:54 PM   #5
JJboy's Avatar
I removed sensing bulb but temperature and pressure have not changed. I'm trying to find the TXV replacement. I can't find online.
Condenser: 12ACB48-3P
Evap:C23-51FC-1
Old 05-28-2011, 04:05 PM   #6
AKA HVACTECHFW
contact cozyparts
IT IS WHAT IT IS
Old 05-28-2011, 06:47 PM   #7
Hvac Pro
yuri's Avatar
Rewards Points: 1,764
Usually there is a 5 digit part # on the sticker or valve itself like "97F56". You need that number to give them and they will match it or cross reference it to the new part# and valve. May need a magnifying glass and to look REAL closely to find it.
Old 05-28-2011, 06:57 PM   #8
JJboy's Avatar
I found online 26K35. I'll check next week.......Yuri, any input about what I said bad TXV?
why the pressure is different when the system is not running?
Old 05-28-2011, 07:04 PM   #9
An old Tradesmen
Rewards Points: 6,836
That digital manifold can do SH and SC. Use its features.
Old 05-28-2011, 07:07 PM   #10
Coil still frozen?
JJ no need to special order a txv,just pick one up at a local supply house. The only time you need an OEM one is if it's still in warranty
Old 05-28-2011, 07:11 PM   #11
Hvac Pro
yuri's Avatar
Yep. You need to completely defrost it and start all over. If a TX valve fails and it is rare with the old ones it will pump down when it starts. Ie: suction pressure should drop quickly while discharge is rising above what is normal (that depends on OAT and load). Need to monitor that at startup. I hate digital gauges and can't tell what you got for readings there. Dial ones and a PT chart is my method. Too much info overload with fancy gadgets is not for me. I like to see the needle move/pulsate/fluctuate and can get a feel for what the compressor is doing. Hard to teach an old dog new tricks.
The first time you get a load of "blue leak lock" or some other crap a guy put in schraeder valves to seal them and it wrecks those fancy gauges you may see why I avoid them.
Old 05-28-2011, 07:24 PM   #12
JJboy's Avatar
Old 05-28-2011, 07:25 PM   #13
JJboy's Avatar
Originally Posted by Marty S. View Post
Coil still frozen?
No
So I just need to know the Ton?
Old 05-28-2011, 07:32 PM   #14
Hvac Pro
yuri's Avatar
It may be a LOT easier for you if you get the OEM one. Should have the same dimensions and fit w/o any alterations. Most of the new Lennox units have special teflon gaskets/o-rings etc so unless that one uses straight flare fittings I would recommend OEM parts until you get a few yrs experience under your belt. Same thing with motors and cond fan motors. Once you understand wiring REAL well then you can use generic parts confidently is my advice.
The Following User Says Thank You to yuri For This Useful Post:
JJboy (05-28-2011)
Old 05-28-2011, 07:39 PM   #15
JJboy's Avatar
The suction pressure change from 50psig ( not running ) to 12psig ( running )
Choosing a Refrigerator based on Repair Value 1655graff Appliances 5 03-01-2011 08:49 AM
Wiring Tradeline L6006C Aquastat to Lennox CBWMV Hydronic Air Handler VIPSpecialNeeds HVAC 5 03-15-2010 06:37 PM