Old 06-15-2012, 01:25 AM   #1
keeps burning out a relay for the outside condensor motor
having trouble at work this one place keeps burning out a relay for the outside condensor motor been there 4 times Cannot figure out what the hells causing this to happen its driving me insane we put a little fuse popper on the circuit to protect it from burning out again but thats just putting a bandaid on it for now I gotta quit running the **** through my mind!It works great while your there everythings drawing the right amps running good like clockwork in 2 days they call again!
any ideas??????
chrisachvac is offline   Reply With Quote
Old 06-15-2012, 06:04 AM   #2
An old Tradesmen
Someone put a larger condenser fan motor in?
Old 06-15-2012, 07:03 AM   #3
nope all original parts motor runs fine not too many amps its the control coil of the relay that keeps failing 208-240 volt coil I have 211 volts to that somethings rotten in denmark anyways no matter if the thing goes they can still run one of the indoor units its a duel zone mini split samsung Ill think on it this weekend they make relays that sense amp draw instead of using voltage that would cure the problem just have to do a little creative rewiring pretty much got the wiring diagram impressed in my brain now!
Old 06-15-2012, 01:13 PM   #4
It was a dark and stormy
Yoyizit's Avatar
Coil is failing by shorting or failing by opening?
High temps. cause insulation to fail.
DC coil resistance is lower than AC coil impedance and may not accurately predict coil current.
All electromechanical relay armatures are pulled in by current but potential relays have a high coil resistance and a narrow pull-in to drop-out range.
If the steady-state values read OK you could have 120v transients going into the coil due to an intermittent short. If they are short enough the fuse may not melt.
Don't change circuitry until you solve this. There is something that you are assuming that is not true. The work is to find out what it is.
Old 06-15-2012, 09:09 PM   #5
Missouri Bound's Avatar
What voltage is available at the equipment? I'm of the opinion that somewhere along the line some wires got switched around and you may have an instance where there is an excessive voltage put to the coil when some other switching is taking place. There is a surge of some kind creating this problem. Any other equipment having this issue? Is there a schematic on the equipment that you can use to verify all connections? It looks bad to keep coming back to fix the same thing over and over.
Do you want it your way or the right way?
power surge with 120v relay astetson Electrical 8 01-16-2012 11:46 PM
Help with baseboard heater relay 98mrd Electrical 20 12-29-2011 02:00 PM
Electric Baseboard Heat - relay problem? sporkman HVAC 7 11-21-2010 07:43 PM
Wiring a Honeywell RA89A Relay shawnmd HVAC 7 10-21-2010 07:58 PM
newbie...relay problems jfabes Electrical 11 05-06-2008 05:48 PM