Old 11-22-2011, 10:16 AM   #1
Keeprite inducer moter has water in it, low pressure switch fault
I have a new 90mvx model that I installed. It ran fine until one day the blower motor would come on, igniter light up, gas for 10 secs then it would shut off. I would then see the three flashes on the led telling me pressure switch. I jumped out the switch and it worked!
For a while anyhow.
It seems there is a LOT of water in the fan and I can hear the motor working hard to get up to speed.
All the drain hose are connected but there is nothing to drain the fan cage.
What the heck did I do wrong?
rbfox is offline   Reply With Quote
Old 11-22-2011, 11:33 AM   #2
There should be a conection between the inducer box and the condensate trap in the unit. Be sure that your drain hose is not plugged up outside the furnace and that it is not double trapped on its way to the drain. You could remove the drain hoses between the inducer housing and the trap and see if the water will come out there, if it does you need to find the problem downstream. If not then you need to clear the obstruction in the inducer housing.
HVACDave is offline   Reply With Quote
Old 11-23-2011, 12:55 AM   #3
Figured it out. I was not level and the water was not draining.
All good now!!
Thanks for the help!!
Changing A Double Switch to a single pole switch and a dimmer switch loydbrahn Electrical 0 11-09-2011 12:00 AM
comfort maker inducer fan/exhaust moter is dripping water? rickwest59 HVAC 10 10-12-2011 04:07 PM
Water Pressure Switch Selection atw58 Plumbing 5 10-07-2011 04:09 PM
Carrier Infinity 69 Trouble Code 42 bodya1 HVAC 4 12-05-2010 07:43 PM
Low/No Hot Water Pressure after changing Elements Onehipcat Plumbing 18 08-05-2010 10:16 AM