Keeprite Furnace Main Blower Problem - HVAC - DIY Chatroom Home Improvement Forum
Old 11-24-2010, 09:15 PM   #1
Keeprite furnace main blower problem
THE BLOWER WORKS FINE ON manual.......comes on ok when air cond is on.....problem is when furnace is on ....the firing cycle starts ok,,,,,,,,,,but blower doesnt come at all.........furnaces shuts down .on..excessive heat..I have replaced fan control module'''no differance.....this an mid-efficency furnace,,,,,,,,spark ignition......I swapped module to test it ..same problem..........I ordered a new relay but don,t think it could be
the problem ..unless there set of contacts that aren,t in use with manual or on A/C..............What am I missing..........we have heat ...just by leaving fan on manual......it all works fine
coyhunter is offline   Reply With Quote
Old 11-24-2010, 10:04 PM   #2
GC/Master Plumber/Mech
Rewards Points: 560
Model please
John Wayne once said "Life is tough and it is even tougher if you are stupid"
Tempstar and Trane Dealer
Old 11-25-2010, 03:52 AM   #3
An old Tradesmen
Rewards Points: 8,170
Do you have a multimeter. And know how to use it.
Old 11-25-2010, 03:17 PM   #4
Originally Posted by Plumber101 View Post
Model please
model #CGKO75N''....
YES i HAVE A MUTI-METER.........CAN CHECK MOST THINGS WITH IT;;
THANKS FOR ANY HELP
Old 11-27-2010, 10:30 PM   #5
could be windings problem
one set of windings could be shot..I am told
Old 11-28-2010, 07:00 AM   #6
An old Tradesmen
Its possible one set of windings is open.
Check to see if the motor is getting voltage from the board in heat mode. And if it is. If your meter can't check a capacitor. I'd still try a new capacitor, before I bought a new motor.
The Following User Says Thank You to beenthere For This Useful Post:
coyhunter (11-28-2010)
Old 11-28-2010, 09:58 AM   #7
keeprite motor
if the capacitor was shot ...would it still run on manual and in the A/C mode.............because it is fine in manual and A/C
Old 11-28-2010, 10:02 AM   #8
AKA HVACTECHFW
Rewards Points: 1,208
its not the capacitor if it runs fine in other modes
hvactech126 is offline   Reply With Quote
Old 11-28-2010, 10:26 AM   #9
An old Tradesmen
Generally not.
But once in a while. A motor will start in one speed with a weak or bad capacitor, but not in another speed.
coyhunter (11-29-2010)
Old 11-29-2010, 05:35 PM   #10
will keep us all posted as i have time
Old 11-30-2010, 05:55 PM   #11
crazy voltage
I checked the high tap setting the black wire to white 119 volts and there also 148 vots between white and blue at the same time this is the 2nd highest speed winding,,,,,,,,,,,,,how is this possible..how can both windings be powered at the same time???
Old 11-30-2010, 07:20 PM   #12
AKA HVACTECHFW
the motor is creating an artificial voltage through another winding, hard to get into the specifics of it, but it's ok......... both windings are not powered
Old 12-01-2010, 04:47 AM   #13
An old Tradesmen
The windings are not electrically separated inside the motor as the term windings implies.
You are probably picking up the back feed from the start winding when the motor is running. The capacitor lead white the white strip is connected to the common lead inside the motor. The other lead is connected to the start winding(which while the motor is running becomes an auxiliary winding). Its an effect that gives PSC motors their efficiency.
Bryant Furnace main burner goes out after 5 seconds Da_Bears HVAC 8 01-03-2012 01:24 AM
Carrier 58SXA main burner problem... bfordmn HVAC 5 11-12-2011 09:14 AM
Trane Furnace Blower Running Nearly Continuously stephensandlin HVAC 3 01-03-2010 01:21 AM
Strange Problem with My Furnace chenjijc HVAC 14 11-04-2009 09:05 PM
Problem with Trane gas furnace quovadis HVAC 17 12-22-2008 01:12 PM