Just Had Compressor Replaced, But Problem - HVAC - DIY Chatroom Home Improvement Forum
Old 07-26-2011, 09:08 PM   #1
Just had Compressor Replaced, but problem
I just had a shorted compressor replaced. This is a 2 piece unit. It seems to cool fine for an hour or so, but then stops cooling completely. It was running for about 45 minutes and was 76 at the return and about 55 at the vent. I left the house for an hour and a half. Temps were 77 and 77. Could it just be low on freon? I plan to call the HVAC company tomorrow.
Fisher252 is offline   Reply With Quote
Old 07-26-2011, 09:24 PM   #2
JJboy's Avatar
Blower motor is just circulation the air, not cooling. You need to check outside unit.
**Always kill the power ** Hot air rises, but heat will always move from higher to lower temperatures. ** Real man shoot in manual. ** If it ain't grounded, it ain't dead.
JJboy is offline   Reply With Quote
Old 07-27-2011, 07:57 AM   #3
The fan on the outside unit is running. Anyone know if low freon will act like this?
Old 07-27-2011, 08:09 AM   #4
JJboy's Avatar
low refrigerant. You should check if the coils are clean.
Old 07-27-2011, 08:12 AM   #5
So, are you saying that low refrigerant will cause this?
Old 07-27-2011, 08:15 AM   #6
JJboy's Avatar
at this point, the tech needs to hook up the gauge and check pressures. temps, and Superheat and subcooling
Did the AC work correctly after you replace the compressor?
Old 07-27-2011, 08:24 AM   #7
It was replaced Monday. I was gone when the tech finished up. When I got back a couple hours later, it was blowing warm air. It was too late to call. I turned the system off. Yesterday, I turned it on around 5:30 PM, and it seemed to be working fine, then I left around 6:15. Got back home at 7:30 and it was blowing warm air again.
Old 07-27-2011, 08:42 AM   #8
JJboy's Avatar
In such case, You need to ask the service man. The line set was cleaned properly , pump down. If the lineset has any "dirty", it will cause this problem.
Old 07-27-2011, 05:43 PM   #9
It was a rainy day when the compressor was replaced. The driers were off the line for about 15 minutes while it was raining. Would that be an issue?
Old 07-27-2011, 05:54 PM   #10
JJboy's Avatar
It was evacuated to 500 microns, no problem.
Old 07-27-2011, 05:58 PM   #11
Could be whatever killed the first compressor is trying to do the same with the new one. Shut it off until the guy comes back out.
Old 07-27-2011, 06:05 PM   #12
How do you know that it was evacuated to 500 microns?
Old 07-27-2011, 06:13 PM   #13
JJboy's Avatar
Using a micron gauge during the evacuation. Many technicians (old school) does not use it. But it does not compromise the AC.
Old 07-28-2011, 07:46 AM   #14
So, does anyone have any idea what this could be? After 1-2 hours of running, the compressor cuts off but the fan on the outside and inside unit continue to run.
Old 07-28-2011, 08:11 AM   #15
fabrk8r
fabrk8r's Avatar
Possible low refrigerant charge. This could be due to a leak created when the new compressor was installed or it may be due to a preexisting leak which may be what caused the original compressor to need replacement.
You need to have a good HVAC technician look at the system.
The system needs to be checked for leaks and proper pressures.
If a leak exists, and it is substantial, the remaining refrigerant may need to be recovered, the leak repaired, new liquid line filter-drier installed and the system vacuumed to at least 500 microns before being recharged again.
The company that installed the new compressor should stand behind their repair.
"The physician can bury his mistakes, but the architect can only advise his clients to plant vines." -- Frank Lloyd Wright
fabrk8r is offline   Reply With Quote
2 TVs fried: Electrical vs. Comcast Coax Cable Problem LynOprinka Electrical 17 07-16-2012 08:01 PM
Very Strange Shower Drain Problem MattWhite Plumbing 12 05-21-2011 11:53 AM
Don't understand this breaker tripping problem majesticjess Electrical 10 03-05-2010 06:42 PM
Stymied by window leakage problem. Matth3w General DIY Discussions 5 06-11-2008 06:26 PM
Post-Tension Slab Problem Advice/Help Mike McBride Building & Construction 2 01-09-2007 01:51 PM