Issue With Compressor Unit - HVAC - DIY Chatroom Home Improvement Forum
Old 08-29-2012, 09:00 PM   #1
Issue with compressor unit
The fan of the compressor is always running, but the compressor never kicks in. By reading around, I figured the cap needs replacing so thats why the compressor never starts, but why is the fan always spinning?
So looking at the schematic, 3 wires head to the compressor. One is power, one is ground, and I assume the third one is the control signal. The spec sheet of the compressor doesn't say anything about the control, but looking at the specs for other compressors, I assume (or hope) that it is universally 24v? My line is always 3V/60hz, no matter if the AC is off or I turn it on.
So could it be a capacitor that needs replacing, or the signal being sent to the compressor that is off?
Thanks for any help.
boast is offline   Reply With Quote
Old 08-29-2012, 09:15 PM   #2
Capacitor
If the fan is running you have more than 3 volts floating around there somewhere so I would be careful. If you have a capacitance tester then it should be checked but if you don't they are very cheap so you can just go to your local supply house and get one and put it on that may be the problem. If it isn't there are a couple of different thing to check. You need to make sure all the wires to the compressor from the terminal block to the capacitor to the contactor. If so then the windings on the compressor need to be checked for continuity. The windings my be burned open or one of the wires in the circuit could possibly be broken.
marcusjson is offline   Reply With Quote
The Following User Says Thank You to marcusjson For This Useful Post:
boast (09-03-2012)
Old 08-29-2012, 10:04 PM   #3
An old Tradesmen
Rewards Points: 7,816
There is no 24 volt wire that goes to the compressor terminals. They are all line voltage. Non of them are a ground either. You have a common, run and start.
Tags
compressor , control signal
HVAC condensor fan outside intermittant wheelsup HVAC 21 05-24-2012 10:25 AM
Westinghouse furnace issue joe8918 HVAC 9 12-04-2011 05:50 PM
how to reduce mositure issue on basement? diy001 Building & Construction 0 10-28-2011 12:44 PM
Perplexing AC issue AvalonGirl HVAC 22 08-17-2011 06:49 PM
CSST Gas Line Lightning Strike and Electrical Issue duteberta Electrical 18 07-29-2009 05:01 PM