Internal Comfort Product Heater Burner On And Off Every 10 Secind - HVAC - DIY Chatroom Home Improvement Forum
Old 02-20-2013, 08:50 PM   #1
internal comfort product heater burner on and off every 10 secind
Hello,
I have a international confort producr COMFORTMAKER heater in my house. ANd noticed that burner is on for 10 second and off for 3 second and do continously. Think something wrong but do not know waht is going on. Sometime blower not on when in auto mode then hear clicking sound all the time then when I turn fan on then blower start. Is this thermo controller problem of some kind of sensor in the furnace.
Please Help
Thank you
gibsonia is offline   Reply With Quote
Old 02-20-2013, 09:30 PM   #2
Roofmaster
Rewards Points: 2,172
What Model Comfortmaker do you have?
Old 02-20-2013, 09:37 PM   #3
Evaportor coil model No. EEA60J22A1
Case Model No. EED60J22C1
MFG No. EED60J22C1
Old 02-20-2013, 09:55 PM   #4
Roofmaster
We need the model number of the Furnace. Probably inside the furnace after you remove the panels so you can see the inducer fan and gas valve. Maybe to the left?
Make sure your flue and intake is clear, and your condensate lines and trap is clear.
Is your filter clean? How often do you change it?
Old 02-20-2013, 10:02 PM   #5
Two model number inside
FBF075F16G1
NTG3075HFG1
And eqipped with electronic air cleaner.
Cleaned about 3 month ago.
Old 02-21-2013, 05:20 AM   #6
An old Tradesmen
Rewards Points: 6,906
EAC's should be cleaned every 30 days, including the pre filters.
May have a problem with the exhaust and the pressure switch is opening and closing.
Old 02-21-2013, 07:34 AM   #7
Roofmaster
Clean your AC Evaporator coil. It sounds like you have an overheating condition, and this could be caused by dirt clogging up your coil.
Old 02-21-2013, 04:27 PM   #8
An old Tradesmen
High limits don't reset in 3 seconds.
His coil may be dirty, but it is not the cause of the symptom he described.
The Following User Says Thank You to beenthere For This Useful Post:
jagans (02-21-2013)
Old 02-22-2013, 09:26 AM   #9
I agree to beenthere my coil is dirty but that caused this problem. When outside temperature is cold burner working continuously until it reached certain temperature (I set temp. to 68) and when outside temperature is warmer a lot of time burner turn on and off intermediately every 5-10 second for about 3 to 5 minute. Then blower never on then system off and keep doing this cycle until I switch fan auto to on then still burner kick on and off several times. The clicking sound is loud I can hear from the first floor where heater is located in basement.
Old 02-22-2013, 09:32 AM   #10
Roofmaster
"I agree to beenthere my coil is dirty but that caused this problem."
Does this really make sense to you?????
Old 02-22-2013, 09:37 AM   #11
Sorry for this sentence.
I mean my coil might be dirty but that not cause this problem.
Old 02-22-2013, 10:21 AM   #12
Roofmaster
Do you mean:
"I agree with Beenthere. My coil is dirty, but that is not what caused my current problem."
So you know your Evaporator coil is dirty, preventing proper airflow out of the furnace, but you are not going to clean it.
Beenthere might very well be correct, as I have followed his posts, and found him to be an excellent HVAC professional.
It is my opinion that dirt, debris, and corrosion are usually the culprits that cause the original problems in the first place, so getting your unit as clean as possible is always the starting point for logical deductive reasoning.
I think Beenthere will second me on this train of thought.
Old 02-23-2013, 07:54 AM   #13
Found small water in the pressure switch line. I cleared the line then no clicking sound and no turn on and off burner. In this case pressure switch has to be changed?
Old 02-23-2013, 09:50 AM   #14
Roofmaster
The water built up so high in your collector box due to lack of service that it flowed into your pressure switch. I would definitely replace it, after a thorough cleaning of your system, including your secondary heat exchanger. and all lines.
www.pexsupply.com
Old 02-23-2013, 05:50 PM   #15
An old Tradesmen
Always best to replace a pressure switch one it gets water in it.