-   -   internal comfort product heater burner on and off every 10 secind (http://www.diychatroom.com/f17/internal-comfort-product-heater-burner-off-every-10-secind-172523/)
gibsonia 02-20-2013 08:50 PM
Hello,
I have a international confort producr COMFORTMAKER heater in my house. ANd noticed that burner is on for 10 second and off for 3 second and do continously. Think something wrong but do not know waht is going on. Sometime blower not on when in auto mode then hear clicking sound all the time then when I turn fan on then blower start. Is this thermo controller problem of some kind of sensor in the furnace.
Please Help
Thank you
jagans 02-20-2013 09:30 PM
What Model Comfortmaker do you have?
gibsonia 02-20-2013 09:37 PM
Evaportor coil model No. EEA60J22A1
Case Model No. EED60J22C1
MFG No. EED60J22C1
jagans 02-20-2013 09:55 PM
We need the model number of the Furnace. Probably inside the furnace after you remove the panels so you can see the inducer fan and gas valve. Maybe to the left?
Make sure your flue and intake is clear, and your condensate lines and trap is clear.
Is your filter clean? How often do you change it?
gibsonia 02-20-2013 10:02 PM
Two model number inside
FBF075F16G1
NTG3075HFG1
And eqipped with electronic air cleaner.
Cleaned about 3 month ago.
beenthere 02-21-2013 05:20 AM
EAC's should be cleaned every 30 days, including the pre filters.
May have a problem with the exhaust and the pressure switch is opening and closing.
jagans 02-21-2013 07:34 AM
Clean your AC Evaporator coil. It sounds like you have an overheating condition, and this could be caused by dirt clogging up your coil.
beenthere 02-21-2013 04:27 PM
High limits don't reset in 3 seconds.
His coil may be dirty, but it is not the cause of the symptom he described.
gibsonia 02-22-2013 09:26 AM
I agree to beenthere my coil is dirty but that caused this problem. When outside temperature is cold burner working continuously until it reached certain temperature (I set temp. to 68) and when outside temperature is warmer a lot of time burner turn on and off intermediately every 5-10 second for about 3 to 5 minute. Then blower never on then system off and keep doing this cycle until I switch fan auto to on then still burner kick on and off several times. The clicking sound is loud I can hear from the first floor where heater is located in basement.
jagans 02-22-2013 09:32 AM
"I agree to beenthere my coil is dirty but that caused this problem."
Does this really make sense to you?????
:huh:
gibsonia 02-22-2013 09:37 AM
Sorry for this sentence.
I mean my coil might be dirty but that not cause this problem.
jagans 02-22-2013 10:21 AM
Do you mean:
"I agree with Beenthere. My coil is dirty, but that is not what caused my current problem."
So you know your Evaporator coil is dirty, preventing proper airflow out of the furnace, but you are not going to clean it.
Beenthere might very well be correct, as I have followed his posts, and found him to be an excellent HVAC professional.
It is my opinion that dirt, debris, and corrosion are usually the culprits that cause the original problems in the first place, so getting your unit as clean as possible is always the starting point for logical deductive reasoning.
I think Beenthere will second me on this train of thought.
gibsonia 02-23-2013 07:54 AM
Found small water in the pressure switch line. I cleared the line then no clicking sound and no turn on and off burner. In this case pressure switch has to be changed?
jagans 02-23-2013 09:50 AM
The water built up so high in your collector box due to lack of service that it flowed into your pressure switch. I would definitely replace it, after a thorough cleaning of your system, including your secondary heat exchanger. and all lines.
www.pexsupply.com
beenthere 02-23-2013 05:50 PM
Always best to replace a pressure switch one it gets water in it.