Intermittent Limit Switch Issue. - HVAC - DIY Chatroom Home Improvement Forum
Old 08-23-2013, 11:18 PM   #1
I'm Your Huckleberry
Rewards Points: 2,270
Goodman GUPI100-4 gas furnace.
Original call, no power, blown transformer, installed new. Next day call back, outside unit not running. No led, btw. Inducer and blower on only while on call for cool. Check for 24 to ground on secondary limit terminals (limit hooked to board) and good to go, continuity, closed. Primary limit nothing. Pull switch wires off of board and check to ground, one shows 24 volts, 26.2 actually but that's irrelevant, and the other spade on the board shows nothing.
Brand new gator clip, jumped from terminal to terminal and limit switch loop still open..?? Brand new control board, too, I should mention. Actually two new boards, Goodman tech support said the first brand new board (I thought original existing board was bad as with limit loop jumped on original board it was still acting like it was open, inducer and blower on only) was bad so I got another one. Today, with second new board in place, they had me remove 24 volts from stat and said if the system turned off the stat was the problem. It powered off so I changed the stat, same issue.
They were also talking about taking the 24 volt transformer common to furnace chassis before telling me the stat was bad which I have not done, yet.
Thanks.
Thanks.
Doc Holliday is offline   Reply With Quote
Old 08-23-2013, 11:49 PM   #2
An old Tradesmen
Rewards Points: 6,588
Check for bad/poor equipment grounding. Check polarity coming to the furnace. Find out if any electrical work was done in the last few months.
The Following User Says Thank You to beenthere For This Useful Post:
hvactech126 (08-23-2013)
Old 08-24-2013, 12:06 PM   #3
Hvac Pro
yuri's Avatar
Rewards Points: 1,454
check the wiring diagram on the back of one of the doors or get one from Goodman. must have some mixed up wiring. may have some mixed up wiring to the tstat or pinched/shorted to it. if R and W get mixed up the heat can still work but no AC. sounds more like a bad wiring to the tstat issue 2 me. I have had pinched wiring get bare and hit metal ducts and have intermittent shorts or cats chew it etc etc. may need a new wire to the tstat.
Old 08-29-2013, 10:55 AM   #4
The polarity thing is one thing I did not check nor did I ever ground the transformer common. No matter, another company and another tech from my company both could not figure it out so they're getting a new furnace.
Thanks.
Old 08-29-2013, 04:41 PM   #5
An old Tradesmen
Better hope it isn't a problem back at the panel box. or the new furnace may not work either.
You know, you could visit us more then once every 6 days.
Old 08-29-2013, 06:36 PM   #6
biggles's Avatar
keep in mind the solid state board needs to see a sequence on HEAT call IDF blower ON, Pressure switch closes spark then the burner runs...jumping the switch confuses the board in the heat cycle call..jump it right after the IDF starts..
Old 08-29-2013, 07:19 PM   #7
Hvac Pro
yuri's Avatar
The problem could be a poor connection in one of the molex plugs if it had them. Sometimes they don't seat properly or get corroded. Have to pull them apart and examine them with a magnifying glass and reseat them properly. Good chance that unit had popped compression rings in the heat ex if it was one of them. Goodmans can be a bit different as they put the limit in series with the gas valve on the newer ones. Jobs like that can drive a person CRAZY
Old 08-29-2013, 07:37 PM   #8
I've been living with my cookoo girlfriend for three months and I don't know my password for this site, can't log in from anywhere other than from on my home pc as it has it remembered.
I hope the new furnace doesn't work either! That'd be a hoot!
Thanks.
Old 08-29-2013, 07:48 PM   #9
An old Tradesmen
Are you using IE, FF, or Chrome? Its easy to find out your password in Chrome.
Old 08-29-2013, 07:50 PM   #10
chrome. do tell!
Thanks.
Old 08-29-2013, 09:52 PM   #11
An old Tradesmen
Go to the control tab on the right side and click it. Then click settings. Scroll down to passwords and forms. Click manage saved passwords. Then when the new box opens, scroll to DIYCHATROOM, click it, then click show. To show you the password.
Lennox Furnace - Primary or Secondary Limit Switch Open georgemeaders HVAC 4 12-12-2012 08:21 PM
Kitchen Light Switch Issue VAGuy Electrical 1 06-24-2012 04:03 PM
American Standard intermittent inducer problem with presssure switch warning no such user HVAC 5 12-26-2011 06:20 PM
fan/light switch buzzing mjlocat Electrical 4 05-23-2010 03:44 PM
3-way light with a twist Jeepsail Electrical 14 05-18-2010 02:24 AM